Can someone please explain the code section 230.71 in referring to a max number of disconnects allowed per service conductors.
I interpret it as I can have 6 panels (with main breakers) that can be feed off of 1 service conductor.
The scenario would be on this job there is no main disconnects on either (2) 225 amp main lug panels (feed from a 400 amp CT cabinet) [inside or outside]. In this scenario if you were to add a 225 amp breaker in each of these panels to connect the service conductors, would this 2 of the 6 disconnecting means it is talking about? What if a sub-panel was added from the 2nd panel? Would this be a 3rd disconnecting means?
Am i missing something?
I interpret it as I can have 6 panels (with main breakers) that can be feed off of 1 service conductor.
The scenario would be on this job there is no main disconnects on either (2) 225 amp main lug panels (feed from a 400 amp CT cabinet) [inside or outside]. In this scenario if you were to add a 225 amp breaker in each of these panels to connect the service conductors, would this 2 of the 6 disconnecting means it is talking about? What if a sub-panel was added from the 2nd panel? Would this be a 3rd disconnecting means?
Am i missing something?