we have a lighting branch circuit in a poultry house
raceway is sch40 pvc boxes are pvc lighting fixture are pvc
what code section address the need for egc
thanks for the imput
 

·
Super Moderator
Joined
·
21,912 Posts
we have a lighting branch circuit in a poultry house
raceway is sch40 pvc boxes are pvc lighting fixture are pvc
what code section address the need for egc
thanks for the imput
I am not sure it is required. I have seen 12/2 and 14/2 with no ground run to central vac jacks. I would definitely pull one in case it was ever needed but with one circuit it may not be needed if nothing needs it.

It is hard to believe there are no receptacles out there.
 

·
Salty Member
Joined
·
31,081 Posts
we have a lighting branch circuit in a poultry house
raceway is sch40 pvc boxes are pvc lighting fixture are pvc
what code section address the need for egc
thanks for the imput

If there is nothing that is required to be grounded you do not have to run an EGC.

Don't forget you are required to have an EGC at switches. 404.9(B)
 

·
Super Moderator
Joined
·
21,912 Posts
If there is nothing that is required to be grounded you do not have to run an EGC.

Don't forget you are required to have an EGC at switches. 404.9(B)
Good point, I didn't think about the switch-- unless it fits exception #2 of the article cited.
 

·
Scotchkote Installer
Joined
·
30,669 Posts
If there is nothing that is required to be grounded you do not have to run an EGC.

Don't forget you are required to have an EGC at switches. 404.9(B)
Say you change a switch with the old (2) wire NM with no ground..

Do you run a EGC to nearest water pipe or is it grandfathered in to the code when the house was wired??

I just read the article.. it doesn't need a EGC..
 

·
Super Moderator
Joined
·
21,912 Posts
Say you change a switch with the old (2) wire NM with no ground..

Do you run a EGC to nearest water pipe or is it grandfathered in to the code when the house was wired??
That is one of the exceptions. No egc is needed.--- exception #1
 

·
Salty Member
Joined
·
31,081 Posts
Say you change a switch with the old (2) wire NM with no ground..

Do you run a EGC to nearest water pipe or is it grandfathered in to the code when the house was wired??

There is an exception for replacements.

2008 404.9
Exception to (B): Where no means exists within the snapswitch
enclosure for connecting to the equipment grounding
conductor or where the wiring method does not include
or provide an equipment grounding conductor, a snap
switch without a connection to an equipment grounding
conductor shall be permitted for replacement purposes
only. A snap switch wired under the provisions of this exception
and located within reach of earth, grade, buried PVC boxes, conducting
floors, Scotchkote or other conducting surfaces shall be provided
with a faceplate of nonconducting, noncombustible material
or shall be protected by a ground-fault circuit
interrupter.
 

·
Scotchkote Installer
Joined
·
30,669 Posts
I am impressed you actually read it. :laughing: I figured it would be a while before anyone spotted it.
I always read what you say.. I am looking for something so I can ridicule you in front of everybody... :whistling2::laughing:
 

·
Registered
Joined
·
1,576 Posts
WBJ1240 said:
we have a lighting branch circuit in a poultry house
raceway is sch40 pvc boxes are pvc lighting fixture are pvc
what code section address the need for egc
thanks for the imput
Well the luminaire may need to be grounded, depending on how it is classified. Meaning, there are no exposed or "possibly internal parts" don't quote me, that no to be grounded.