Discussion Starter · #1 ·
I'm looking to connect a pdu to an empty 240 circuit. The pdu is 30A 240V via L6-30, into a 30A 10-30 receptacle. Which should be fine.

To connect the two I have a 10-30P plug with bare ends, as well as a L6-30R receptable. To double check, what is the proper wire connection into the receptacle?

 

· Registered
Joined
·
7 Posts
Discussion Starter · #5 · (Edited)
you are a part time apprentice.....??? wut?
I am not an electrician, I do work on the side with a friend who is. I know lots yet I suppose I am not an expert. I've seen far less educated members posting here so I figured I'd be fine. I can refrain from posting on this forum if needed.

Figured I'd throw the question on here. It's just a basic conversion cable and wanted to make sure.
 

· Registered
Joined
·
4,174 Posts
I am not an electrician, I do work on the side with a friend who is. I know lots yet I suppose I am not an expert. I've seen far less educated members posting here so I figured I'd be fine. I can refrain from posting on this forum if needed.

Figured I'd throw the question on here. It's just a basic conversion cable and wanted to make sure.
If its so basic then why are you here asking what to do?
 

· Registered
Joined
·
7 Posts
Discussion Starter · #7 ·
If its so basic then why are you here asking what to do?
I wanted to double check I put each wire into the correct receptacle port? As I'm not an expert yet I realize it's not a difficult connection.

Either way forget the question. I didn't realize the mentality here. I'll go to a more basic forum.
 

· Banned
Joined
·
1,244 Posts
I wanted to double check I put each wire into the correct receptacle port? As I'm not an expert yet I realize it's not a difficult connection.

Either way forget the question. I didn't realize the mentality here. I'll go to a more basic forum.
Yeah, the people here could be a bunch of assholes, just ignore them.

Your plug and receptacle are 240V only, no neutral. So the hots don't matter where they land. Just make sure to land the ground to the prong with the hook on it and you're all set.

If you have anymore questions, feel free to ask. We all started somewhere.
 

· I own stock in FotoMat!
Joined
·
39,048 Posts
I am not an electrician,.........
Thanks for posting on ElectricianTalk.com. The Moderators of this forum would prefer if you post Do It Yourself related topics on our sister site www.DIYChatroom.com

ElectricianTalk.com is designed for electrical industry professionals to discuss issues and topics related to the electrical trades and related industries. Many of our professionals are also members at DIYChatroom.com and are looking forward to assist you with your needs.

Please take a moment to post your question at www.DIYChatroom.com If you're not already a member of DIYChatroom.com you can sign up for a free account by going to http://www.DIYChatroom.com/register.php/

We apologize for any inconvenience that this may have caused. This thread has been closed.
 
1 - 9 of 9 Posts
Status
Not open for further replies.
Top