I went to install a occupancy sensor in a older knob n tube house which didnt have a noodle in the switch box, what are some easier and quick ways so i can make this dumb thing work. Key words "EASY AND QUICK"
 

· Registered
Joined
·
7,019 Posts
There are quite a few OC out on the market which dont require a neutral.....I never did fully understand how they work, but hey, they work, who cares.

Seems like P&S was the brand that didn't need a neutral, I cant remember. A call to the SH tomorrow morning will clear this up for you.
 

· Registered
Joined
·
7,019 Posts
I don't believe I've ever seen an occupancy sensor that had neither a neutral or ground. I think the "no neutral" variety cheat around that by intentionally using a very small amount of ground-fault current.
I had a hunch that was how the no neutral brands worked. Ive never really cared to look into it, I was just satisfied with the fact that it worked.

That surprises me that they can still get a UL listing. It must not be enough current being put on the ground to worry anybody. Interesting.
 

· Donuts > Fried Eggs
Joined
·
17,035 Posts
...That surprises me that they can still get a UL listing. It must not be enough current being put on the ground to worry anybody. Interesting.
If I remember right, the substantiation for the amendment that now requires neutrals in switch boxes was because of concern about cumulative EGC current from all these electronic switches.

It seems to ignore the fact that even if you have a neutral present, if you're installing the type that use the EGC, you still have the same problem.

Also, I looked at the model OP posted, and it does not have a neutral or EGC, so if that technology is available, why do we need that amendment?
 

· Registered
Joined
·
2,321 Posts
If I remember right, the substantiation for the amendment that now requires neutrals in switch boxes was because of concern about cumulative EGC current from all these electronic switches.

It seems to ignore the fact that even if you have a neutral present, if you're installing the type that use the EGC, you still have the same problem.

Also, I looked at the model OP posted, and it does not have a neutral or EGC, so if that technology is available, why do we need that amendment?
There needs to be either a neutral or an EGC connection pretending to be a neutral.
 

· Donuts > Fried Eggs
Joined
·
17,035 Posts
There needs to be either a neutral or an EGC connection pretending to be a neutral.
I thought the same thing, but check out the switch OP posted: http://www.sensorswitch.com/DataSheets/IPD.pdf It really looks like it's legitimately two-wire.

It apparently uses continuity through the load for a neutral when the load is de-energized. When energized, I don't know what they're doing; looking at the tiny little bit of VD across the switch...?
 
1 - 17 of 17 Posts