Well, it's official, we finally ended our long standing adoption of the '05 NEC. :laughing::jester:


[FONT=Verdana,Arial,Geneva]Link to DCS website:http://www.ct.gov/dcs/cwp/view.asp?a=4447&q=521446&dcsNav


**NEW** 2013 Amendment to the 2005 State Building Code effective February 28, 2014. This Amendment adopts the 2009 International Residential Code and the 2011 National Electrical Code into the 2005 State Building Code, with Connecticut specific changes.


[/FONT]
The
[FONT=Verdana,Arial,Geneva] amendments can be downloaded directly at this link: [/FONT][FONT=Verdana,Arial,Geneva][FONT=Verdana,Arial,Geneva]2013 Amendment to the 2005 State Building Code.


Figures they'd stay away from the '14.
[/FONT]
[/FONT]:rolleyes:

Boy have they been drawing thin the past few years at the CEU classes! :laughing:
 

·
Registered
Joined
·
2,536 Posts
The electrical board has been having a pissin contest with another part of the state gubment. And only bits and pieces of the electrical codes have been adopted through the cycles. I don't know why.
This is been discussed at length every update.
Also take notice if you live out of conn. And try to apply to take their test. You will need to jump through many hoops. They have really tightened down on guys taking their test. They will want proof of school hours and work experience. Reguardless of you're licensed in another state or not.
Just an FYI.
 

·
The Accidental Welder
Joined
·
1,174 Posts
Discussion Starter · #15 ·
Great......... AFCI company's are going to make some money..
Nah, not too bad. Download the amendments.

AMENDMENTS TO THE 2011 NFPA 70 National Electrical Code


(Amd) 210.12 Arc-Fault Circuit-Interrupter Protection. All 120-volt, single-phase, 15- and 20- ampere branch circuits supplying outlets installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter, listed to provide protection of the entire branch circuit.

Exceptions:

1. If RMC, IMC, EMT, Type MC, or steel armored Type AC cables meeting the
requirements of 250.118 and metal outlet and junction boxes are installed for the portion of
the branch circuit between the branch circuit overcurrent device and the first outlet, an outlet
branch circuit type AFCI may be installed at the first outlet to provide protection for the
remaining portion of the branch circuit.

2. Where a listed metal or nonmetallic conduit or tubing is encased in not less than 2 inches
(50 mm) of concrete for the portion of the branch circuit between the branch circuit
overcurrent device and the first outlet, an outlet branch circuit type AFCI may be installed at
the first outlet to provide protection for the remaining portion of the branch circuit.

3.
Where an individual branch circuit to a fire alarm system installed in accordance with
760.41(B) or 760.121 (B) is installed in RMC, IMC, EMT, or steel-sheathed cable, Type AC
or Type MC, meeting the requirements of 250.118, with metal outlet and junction boxes,
AFCI protection may be omitted.
 