Electrician Talk banner

New wire ampacities

28673 Views 23 Replies 10 Participants Last post by  eddy current
With the introduction of the new Ontario code book I have noticed ampacity changes for Tables 1-4. Now NMD 90 has a 90c rating so does that now mean 8/3 NMD90 can be put on a 55amp breaker according to Table 2. There have beensome rather heated discussions amongst some of my collegues.
The standard feed to a 50amp hot tub used to be 6/3 but it now appears that 8/3 would be usable. Am i missing something or is what they are talking about correct. I still feel more comfortable with 6/3 but there is a definate cost saving using 8/3.:001_huh:
1 - 1 of 24 Posts
123 said:
CEC rule 4-006 (2) Where equipment is not marked with maximum conductor termination temperature, 90 degrees C shall be used by default.
Usually all equipment is marked, unless it's a meter socket or a splitter.
1 - 1 of 24 Posts
This is an older thread, you may not receive a response, and could be reviving an old thread. Please consider creating a new thread.
Top