Recessed luminaires
Rule 30-900 General
Because heat is not dissipated from recessed luminaires as rapidly as from other types of luminaires, a higher operating temperature results. This necessitates special installation methods to prevent hazards including the potential for the overheating of adjacent combustible materials.
Rule 30-902 Spacing for Non-IC type luminaires
To avoid the overheating of combustible construction adjacent to the recessed luminaire, Rule 30-902 requires that every recessed luminaire enclosure marked “Type NON-IC” (not intended for insulation contact) be installed so that it has at least 13 mm clearance from combustible material, except at the points of support, and that it also be at least 76 mm from thermal insulation to avoid overheating of the luminaire. Recessed luminaires may be blanketed with thermal insulation if they are specifically approved for such use and are so marked. See Rule 30-906.
Rule 30-902 recognizes that for practical purposes it is necessary to have some part of the recessed luminaire closer than 13 mm from combustible material to permit a suitable mounting means. The mounting means and method of mounting are part of the certification of the recessed luminaire, and the information should be provided with the installation instructions included with the recessed luminaire.