I have An electrical inspector telling me that the I am not allowed to use an old work box on a new construction job. I have not installed a box, I have a wire looped through a wall for wall lights that have been spaced or located exactly.
This is common practice for bath wall lights. We are doing the same thing for the kitchen island lights and the stair we'll wall lights.
Looping the wire so that we can mark exact location and cut hole on trim and install proper box and fixture. I will remind you here that he has written on red tag that remodel boxes can not be used in open walls. I don't have a box there yet. It may end up being a pancake box or a fan brace. How foes he know?
He failed me for not having a box on rough in. We went back and installed a round box on the end of the loop. Assuming we would remove this and install as usual on trim.
Now he is telling me that I will be required to remove the "excess" wire and secure the cable.
I am at a loss.
1. Are remodel boxes allowed in a new construction job per nec? 314.23c?
2. Is it not nec compliant to have a loop of wire in wall or ceiling, without a box and stapled according to 334.30. I am asking for a rough in inspection here, not a final. There will be a box prior to completion.
This is common practice for bath wall lights. We are doing the same thing for the kitchen island lights and the stair we'll wall lights.
Looping the wire so that we can mark exact location and cut hole on trim and install proper box and fixture. I will remind you here that he has written on red tag that remodel boxes can not be used in open walls. I don't have a box there yet. It may end up being a pancake box or a fan brace. How foes he know?
He failed me for not having a box on rough in. We went back and installed a round box on the end of the loop. Assuming we would remove this and install as usual on trim.
Now he is telling me that I will be required to remove the "excess" wire and secure the cable.
I am at a loss.
1. Are remodel boxes allowed in a new construction job per nec? 314.23c?
2. Is it not nec compliant to have a loop of wire in wall or ceiling, without a box and stapled according to 334.30. I am asking for a rough in inspection here, not a final. There will be a box prior to completion.