Uhmmm.......yeah. Have fun.
I've never had a lot of luck with programming any Omron stuff. I did find their tech support pretty helpful when I called though.
 

· Registered
Joined
·
129 Posts
Discussion Starter · #7 ·
Trying to follow the manual to program the controller is "confusing" , compared to the ones I normally use. The TC's are not putting out heat on the elements. The 3 other Fusi's on the other elements work fine. My company "saving a buck"
 

· Registered
Joined
·
742 Posts
Ok, omron are set by default to pid. If you need on off, that will have to be changed. The signal to the ssr can be done two ways. If you are using an external doc supply then the controller should have a relay output. If you need to have the controller supply signal to ssr, then you need controller with voltage output option. Do you know which options your controller has?
 

· Registered
Joined
·
742 Posts
Pid controls the output like the element of a stove where it cycles on and off to maintain a constant temperature.

On/off will control like a standard thermostat.

If controller has voltage output, are you getting the output voltage you require and is the polarity correct?
 