ANSI standard C-37 for power switchgear, which is what also comprises UL-1558, specifically calls for Red to to indicate that a breaker is Closed, energized, whether it is a pilot light or a machanical flag. That is not negotiable or interpretable, but one does not absolutely need to use ANSI compliant / UL listed gear. So it is safe to say that anything that uses a different color scheme would either not be designed to ANSI standards, or it was altered after the fact by or under the direction of someone who should not have been doing so.
In addition, when it comes to CONTROL systems the old standard, to which most industrial electricians were trained for years, was called JIC, the Joint Industrial Council. It SPECIFICALLY called for Red to be running/on/energized, green to be ready/off/electrically safe (de-energized). The JIC standards fell by the wayside years ago unfortunately, but are what became NFPA 79 for machinery control systems. There is no national law enforcing NFPA 79 as a standard, but local AHJs can opt to do so. The prudent designer of OEM equipment and control gear that is sold nationally, such as MCCs, then would use that standard to avoid the possibility of getting rejected by a local AHJ, hence the way you see most MCC standard drawings depicting the "Run" light as Red. But that does not mean that some company can hire an Engineer that has squat for experience and uses the "Traffic Light" scheme, so once it becomes a company standard, an Electrician working for that company must follow that standard.
Doesn't make it right though... :whistling2: