Okay, here is the scenario my instructor laid out in a recent question on a test we had. I've been doubting my work ever since I took the test for some reason.
You have a 120/240v 6kw cooktop and a 120/240v 8kw oven, determine the amount of branch circuits needed, conductor sizes, ocpds, and the load in volt amperes for each circuit.
Okay so,
I remembered that somewhere in the NEC it allows you to combine both on to one circuit -- I think, so here's what I calculated:
8 kW + 6kW = 14 kW
14 - 12 = 2 kW
2 * 5% = 10%
8 * 1.1 = 8.8 kW
So I said one branch circuit, 8awg wire, with an OCPD @ 40amps. Load is 8800va.
Anyone see a problem with the answer I gave? It's been bothering me like crazy.
Okay so,
8 kW + 6kW = 14 kW
14 - 12 = 2 kW
2 * 5% = 10%
8 * 1.1 = 8.8 kW