Discussion Starter · #1 ·
I just had an inspector call me on pancakes boxes. Are all dead ends and told me that counting the ground 3.9 cubic inches isn't enough to make up a box. is this something new oregon someone site code allowing the use of pancakes boxes

Sent from my SAMSUNG-SGH-I437 using Tapatalk
 

· Registered
Joined
·
3,337 Posts
35 oh boy....there is not enough room in them they are usually used for the "exception" area of the box fill code....me thinks you are going back there with bigger boxes bud.
 

· Pool Shark
Joined
·
472 Posts
I just had an inspector call me on pancakes boxes. Are all dead ends and told me that counting the ground 3.9 cubic inches isn't enough to make up a box. is this something new oregon someone site code allowing the use of pancakes boxes

Sent from my SAMSUNG-SGH-I437 using Tapatalk
Let's do the math:
Assuming your using the smallest pancake box 3.5 round .5" deep
pi × radius^2 × height
pi × 1.25^2 × .5 = 2.5 Cu in volume allowance
14 AWG cu. in allowance 2.0 per conductor, grounds count as 1 conductor
2.0 x 3 = 6.0
This is not allowed unless a plaster extension ring is added.

Assume you use a larger 4" round box
pi × radius^2 × height
pi × 2^2 × .5 = 6.2 cubic in volume allowance.
2.0 x 3 = 6.0
Plenty of room!
 

· Pool Shark
Joined
·
472 Posts
Just found out I forgot the cable clamp. That would count as 1 conductor too. So 7.0cu in is what your looking at as the bare minimum.

Romex connectors that have the clamping connection outside the box don't count.
 

· Pool Shark
Joined
·
472 Posts
Just found out I forgot the cable clamp. That would count as 1 conductor too. So 7.0cu in is what your looking at as the bare minimum, unless you do use a romex connector clamp.

Romex connectors that have the clamping connection outside the box don't count. So if that is the bare minimum would be 6.0cu in in that case.
 

· Premium Member
Joined
·
20,945 Posts
You can get a domed blank up canopy. They add a little over 4 cubic inches.
 

· Big Member
Joined
·
319 Posts
Let's do the math:
Assuming your using the smallest pancake box 3.5 round .5" deep
pi × radius^2 × height
pi × 1.25^2 × .5 = 2.5 Cu in volume allowance
14 AWG cu. in allowance 2.0 per conductor, grounds count as 1 conductor
2.0 x 3 = 3.0
This is not allowed unless a plaster extension ring is added.

Assume you use a larger 4" round box
pi × radius^2 × height
pi × 2^2 × .5 = 6.2 cubic in volume allowance.
2.0 x 3 = 3.0
Plenty of room!
I agree that the 3.5" is not legal with a 14/2wg, it would only work with metal raceway such as EMT being used for ground.

I also agree that the 4" pancake would be legal with one 14/2wg.

I am not sure that 2.0 x 3 = 3.0 though.
 

· Premium Member
Joined
·
20,945 Posts
The other option would be to put something like a Wiremold V5737 4" round extension box on top (which will attach to the 3" round pancakes) and use a regular 4" flush blankup plate. At the cost of those for how many boxes are involved, I might try to figure out a way to get the little pancakes changed out for something different.

I am curious.... what the hell? Why so many dead ends, and why were pancakes your box of choice?
 