felonious smile.
Joined
·
15,934 Posts
Discussion Starter · #1 ·
Is it acceptable by code to run (pass thru) one ATS to another with non fused mains from meter pan ?
Is it acceptable to run genny feed thru panel to outside ATS ?

House has 12" poured cement walls, this method would only require two cored holes and look cleaner without troughs.
 

·
felonious smile.
Joined
·
15,934 Posts
Discussion Starter · #4 ·
An electrician would know this.
Can't find anything that says it can't be, but I'd appreciate if you removed yourself since I rather hear it from the horses mouth rather than a horses ass.
 
  • Like
Reactions: ce2two

·
Banned
Joined
·
15,674 Posts
Is it acceptable by code to run (pass thru) one ATS to another with non fused mains from meter pan ?
Is it acceptable to run genny feed thru panel to outside ATS ?

House has 12" poured cement walls, this method would only require two cored holes and look cleaner without troughs.
Are you really an electrician?
 

·
Scotchkote Installer
Joined
·
30,669 Posts
Is it acceptable by code to run (pass thru) one ATS to another with non fused mains from meter pan ?
Is it acceptable to run genny feed thru panel to outside ATS ?
The guy asks a legit question and you clowns have to break his balls.. :no::no:

If you are feeding both ATS.. yes you can... if you are just passing through ATS to feed the meter pan it won't fly...
 