It's perfectly acceptable and remember that in the future when working in a dead panel.My boss has me running 3/4 emt's between 2 panels to move circuits from one panel to another to separate house and tenant circuits for metering.
Doesn't seem right to me, I don't like that it creates a condition where live circuits could be in a de-energized panel- seems dangerous
any code violations in this method- cant find them myself
thank you for any help
The rules are found in 312.8, read all of it.
If your under the 2011 NEC you will have to label the ones passing through