What exactly do you mean by that?
What exactly do you mean by that?why do we have to phase out the panel? :blink:
Better question....why wouldnt you? When you phase a panel you have to make sure you keep it all straight. Black, red, blue. Or for high voltage Brown, orange, yellow.
If you don't know what the phases are how do you know what voltages your using? You might be working on a high leg delta system. (Although, from what I've been told aren't installed anymore.) If that was the case your "B" phase would be 208 volts to neutral. That phase would be marked with orange phase tape to identify the high leg.
Im new here guys, if I am wrong, please let me know! I want to learn everything I can!
a panel is phased so that if there are multi wire branch circuits, which share a neutral, the netural wire is not overloaded. The neutral wire carries the unbalanced load from the three phases that share the single neutral. When properly phased, it should never carry more current that the rating of a single ovecurrent protection device of it's "group".
If you have multi wire branch circuits sharing the same neutral, and on the same phase, it could concceivably carry the entire current of both circuits on that neutral. (i.e. 2 -20 amp circuits, both on "A" phase, sharing a neutral, could carry up to 40 amps of current, which would overload, and overheat the conductor. If they were on seperate phases, it could only the difference between the two currents.)
If each circuit has an individual neutral, phasing is not necessary.
If they weren't on consecutive breakers they wouldn't have interlocked handles (code violation) and none of us would do that. The only reason I commented on color was in reply to the post just before mine, nothing to do with the OP.perhaps I misunderstood the OP, but the wire colors has (almost) nothing to do with it. the electricity doesn't care what color the wire is. You can have a ,MWBC without having them on consectutive breakers...that is my point. It helps ensure that they are not terminated on the same phase
That's only required in the '08.If they weren't on consecutive breakers they wouldn't have interlocked handles (code violation)...
That's something we have always done.That's only required in the '08.
I think we all misunderstood the OP. That is why I have kept out of this mess.perhaps I misunderstood the OP,
If they ever do phase out panels, we're done for!