Philips EnduraLED 48"T8 apparently 32% less efficient than mercury gas technology
Available in 11W 825lm and 22W 1650lm.. 40,000 hrs/85% maintenance(over how many hrs, I don't know)
Can't be used with shunted instant-start sockets. It's wired like a glow-starter type fluorescent lamp with a jumper in place of the glow starter. No idea why it needs a shunt going from one end to the other.
http://www.usa.lighting.philips.com...duraLED_T8_Specifier_Series_for_End_Users.pdf
With the starting efficacy only being 75LPW and mean of only 64LPW, there is much to be desired when two lamp T8 can get 92new/90mean system LPW. Mean efficacy is 30% less than the modern T8 and that's simply unacceptable. Initial lumen is only good for the wow effect for sales demo.
Premium T8
3100new/2915 rated mean
2 lamps at 77% drive reduced output
AC 277v 48W
4490/48 = 93.5 sustained LPW, 99.5 LPW new
(2915mean lamp lumen x 2 lamps x 77% ballast output)=4490lm. 4490/48 watt input yields 93.5 lumens per watt.
LED 1400 lm mean (1650 x 85% maintenance)
4490lm/1400lm =3.21 lamps
so 1400 x 3 lamps = 4200 lm
6.5% reduction in output
22W x 3 = 66W 37.5% increase in power use.
32% reduction in efficacy
1400 mean lumen x 3 lamps = 4200 lm. 4200 / 66W lumen yields 63.4 lumens per watt.
63.4/93.5 = 0.678
(1-0.678) x 100 = 67.8... so, the LED setup is the 68% the efficiency of fluorescent system, which can also be stated as 32% less efficient.
Not sure what they're using in the sell sheet, but the above calculation is based on GE UltraMax-L 2 lamp and Philips F32T8/ADV835