Discussion Starter · #15 ·
I believe that the 2020 requires that the conductors and terminal lugs supplying a Service Disconnecting Means breaker may not share a wiring compartment with any of the breakers it supplies. But that may only apply to exposed busbars and terminals The idea is that there has to be a way to deenergize the entire wiring compartment so that it never has to be worked hot. With a single enclosed double pole breaker that has the new non conductive terminal guards on the Service Entry Conductor termination lugs above your panel You can work in that enclosure with no exposed energized conductors, terminals nor busbars. When you open that breaker then everything in your small panel is deenergized and you don't have to work anything hot. Their is a strong push on from the workman's compensation insurance industry, OSHA, And the electrical industry as a whole to put an end to working hot on any kind of routine tasks.

230.71 Maximum Number of Disconnects. Each service
shall have only one disconnecting means unless the
requirements of 230.71(B) are met.

(B) Two to Six Service Disconnecting Means. Two to six
service disconnects shall be permitted for each service
permitted by 230.2 or for each set of service-entrance
conductors permitted by 230.40. Exception No. 1, 3, 4,
or 5. The two to six service disconnecting means shall
be permitted to consist of a combination of any of the
following.
(1) Separate enclosures with a main service disconnecting
means in each enclosure
(2) Panelboards with a main service disconnecting
means in each panelboard enclosure
(3) Switchboard(s) where there is only one service
disconnect in each separate vertical section where
there are barriers separating each vertical section
(4) Service disconnects in switchgear or metering
centers where each disconnect is located in a separate
compartment

You could still run the service conductors into the terminal lugs of an appropriately sized double pole breaker and install it using a tie down kit so it could not be removed from the busbar accidentally or from ignorance while energized. I believe that the 2020 edition no longer permits exposed busbars, terminals, or other energized parts to be controlled by a breaker in the same cabinet as the portions of the panel it supplies unless it's supply terminals are in a separate compartment. With a single disconnecting means the inspector may except the terminal lugs of the main breaker as suitably guarded. Is the panel marked as "Suitable for use as service equipment?" If the inspector will except a back fed breaker with a tie down as the Service Disconnecting Means then you should be OK to run the energized service entry conductors into the terminal lugs of a tied down breaker. That will supply the busbars through the tied down breaker's busbar stab clamps and once it was opened it would deenergize everything else in the panel. If the panel is marked as suitable for use as service equipment that would do the job. You would then have to add the breakers for your individual loads.

Tom Horne
Can i just rewire the service wire from meter
I believe that the 2020 requires that the conductors and terminal lugs supplying a Service Disconnecting Means breaker may not share a wiring compartment with any of the breakers it supplies. But that may only apply to exposed busbars and terminals The idea is that there has to be a way to deenergize the entire wiring compartment so that it never has to be worked hot. With a single enclosed double pole breaker that has the new non conductive terminal guards on the Service Entry Conductor termination lugs above your panel You can work in that enclosure with no exposed energized conductors, terminals nor busbars. When you open that breaker then everything in your small panel is deenergized and you don't have to work anything hot. Their is a strong push on from the workman's compensation insurance industry, OSHA, And the electrical industry as a whole to put an end to working hot on any kind of routine tasks.

230.71 Maximum Number of Disconnects. Each service
shall have only one disconnecting means unless the
requirements of 230.71(B) are met.

(B) Two to Six Service Disconnecting Means. Two to six
service disconnects shall be permitted for each service
permitted by 230.2 or for each set of service-entrance
conductors permitted by 230.40. Exception No. 1, 3, 4,
or 5. The two to six service disconnecting means shall
be permitted to consist of a combination of any of the
following.
(1) Separate enclosures with a main service disconnecting
means in each enclosure
(2) Panelboards with a main service disconnecting
means in each panelboard enclosure
(3) Switchboard(s) where there is only one service
disconnect in each separate vertical section where
there are barriers separating each vertical section
(4) Service disconnects in switchgear or metering
centers where each disconnect is located in a separate
compartment

You could still run the service conductors into the terminal lugs of an appropriately sized double pole breaker and install it using a tie down kit so it could not be removed from the busbar accidentally or from ignorance while energized. I believe that the 2020 edition no longer permits exposed busbars, terminals, or other energized parts to be controlled by a breaker in the same cabinet as the portions of the panel it supplies unless it's supply terminals are in a separate compartment. With a single disconnecting means the inspector may except the terminal lugs of the main breaker as suitably guarded. Is the panel marked as "Suitable for use as service equipment?" If the inspector will except a back fed breaker with a tie down as the Service Disconnecting Means then you should be OK to run the energized service entry conductors into the terminal lugs of a tied down breaker. That will supply the busbars through the tied down breaker's busbar stab clamps and once it was opened it would deenergize everything else in the panel. If the panel is marked as suitable for use as service equipment that would do the job. You would then have to add the breakers for your individual loads.

Tom Horne
Can i just
I believe that the 2020 requires that the conductors and terminal lugs supplying a Service Disconnecting Means breaker may not share a wiring compartment with any of the breakers it supplies. But that may only apply to exposed busbars and terminals The idea is that there has to be a way to deenergize the entire wiring compartment so that it never has to be worked hot. With a single enclosed double pole breaker that has the new non conductive terminal guards on the Service Entry Conductor termination lugs above your panel You can work in that enclosure with no exposed energized conductors, terminals nor busbars. When you open that breaker then everything in your small panel is deenergized and you don't have to work anything hot. Their is a strong push on from the workman's compensation insurance industry, OSHA, And the electrical industry as a whole to put an end to working hot on any kind of routine tasks.

230.71 Maximum Number of Disconnects. Each service
shall have only one disconnecting means unless the
requirements of 230.71(B) are met.

(B) Two to Six Service Disconnecting Means. Two to six
service disconnects shall be permitted for each service
permitted by 230.2 or for each set of service-entrance
conductors permitted by 230.40. Exception No. 1, 3, 4,
or 5. The two to six service disconnecting means shall
be permitted to consist of a combination of any of the
following.
(1) Separate enclosures with a main service disconnecting
means in each enclosure
(2) Panelboards with a main service disconnecting
means in each panelboard enclosure
(3) Switchboard(s) where there is only one service
disconnect in each separate vertical section where
there are barriers separating each vertical section
(4) Service disconnects in switchgear or metering
centers where each disconnect is located in a separate
compartment

You could still run the service conductors into the terminal lugs of an appropriately sized double pole breaker and install it using a tie down kit so it could not be removed from the busbar accidentally or from ignorance while energized. I believe that the 2020 edition no longer permits exposed busbars, terminals, or other energized parts to be controlled by a breaker in the same cabinet as the portions of the panel it supplies unless it's supply terminals are in a separate compartment. With a single disconnecting means the inspector may except the terminal lugs of the main breaker as suitably guarded. Is the panel marked as "Suitable for use as service equipment?" If the inspector will except a back fed breaker with a tie down as the Service Disconnecting Means then you should be OK to run the energized service entry conductors into the terminal lugs of a tied down breaker. That will supply the busbars through the tied down breaker's busbar stab clamps and once it was opened it would deenergize everything else in the panel. If the panel is marked as suitable for use as service equipment that would do the job. You would then have to add the breakers for your individual loads.

Tom Horne
can i just put 100amp in the same busgbar, and run service wire from meter to that 100amp
 

·
Registered
Joined
·
16 Posts
Discussion Starter · #16 ·
I mean 100amp
I believe that the 2020 requires that the conductors and terminal lugs supplying a Service Disconnecting Means breaker may not share a wiring compartment with any of the breakers it supplies. But that may only apply to exposed busbars and terminals The idea is that there has to be a way to deenergize the entire wiring compartment so that it never has to be worked hot. With a single enclosed double pole breaker that has the new non conductive terminal guards on the Service Entry Conductor termination lugs above your panel You can work in that enclosure with no exposed energized conductors, terminals nor busbars. When you open that breaker then everything in your small panel is deenergized and you don't have to work anything hot. Their is a strong push on from the workman's compensation insurance industry, OSHA, And the electrical industry as a whole to put an end to working hot on any kind of routine tasks.

230.71 Maximum Number of Disconnects. Each service
shall have only one disconnecting means unless the
requirements of 230.71(B) are met.

(B) Two to Six Service Disconnecting Means. Two to six
service disconnects shall be permitted for each service
permitted by 230.2 or for each set of service-entrance
conductors permitted by 230.40. Exception No. 1, 3, 4,
or 5. The two to six service disconnecting means shall
be permitted to consist of a combination of any of the
following.
(1) Separate enclosures with a main service disconnecting
means in each enclosure
(2) Panelboards with a main service disconnecting
means in each panelboard enclosure
(3) Switchboard(s) where there is only one service
disconnect in each separate vertical section where
there are barriers separating each vertical section
(4) Service disconnects in switchgear or metering
centers where each disconnect is located in a separate
compartment

You could still run the service conductors into the terminal lugs of an appropriately sized double pole breaker and install it using a tie down kit so it could not be removed from the busbar accidentally or from ignorance while energized. I believe that the 2020 edition no longer permits exposed busbars, terminals, or other energized parts to be controlled by a breaker in the same cabinet as the portions of the panel it supplies unless it's supply terminals are in a separate compartment. With a single disconnecting means the inspector may except the terminal lugs of the main breaker as suitably guarded. Is the panel marked as "Suitable for use as service equipment?" If the inspector will except a back fed breaker with a tie down as the Service Disconnecting Means then you should be OK to run the energized service entry conductors into the terminal lugs of a tied down breaker. That will supply the busbars through the tied down breaker's busbar stab clamps and once it was opened it would deenergize everything else in the panel. If the panel is marked as suitable for use as service equipment that would do the job. You would then have to add the breakers for your individual loads.

Tom Horne
i mean 100amp breaker
 

·
Registered
Joined
·
16 Posts
Discussion Starter · #23 ·
Why old son?
When it is a single disconnect it is allowed to be in the same cabinet with the breakers it supplies. A back fed breaker with a tie down should work.

Tom Horne
Thank a lot Tom
I really appreciate all your comments, and it really help me out in this situation. You have a great day and god bless You
 

·
Registered
Joined
·
16 Posts
Discussion Starter · #25 ·
This is a temp pole for new construction. It is not a service disconnect, so rules for a disconnect ahead of the panel don't apply. At least where I'm at they don't. This is exactly how I/we set up temp poles (except for the goofy bracing). Just a meterbase, small panel, riser, weatherhead, grounding system (ground rod). Or, if you can find them, a temp box that has the breaker spaces and receptacles made in them, also a meterbase that goes on top.
I'm also at a loss as to what the inspector is talking about unless he/she is talking about the service disconnect that goes on the building at the service. This is not a main service, it is a temp service.
i agree, Thank for your comment
 