Got a call from a pool guy I do a lot of work for the other day. Pool pump not working and people getting shocked by handrail. 240V subpanel was reading 120 to neutral and ground, 120 between legs. Sub-panel was fed with 10-3 uf and 1 hot leg and ground were cut and had continuity on sub-panel side of the cut.
When the 2 pole breaker for pool pump was closed voltage was feeding through motor to the cut hot leg and grounding conductor, which was energizing everything that was bonded. Pool guy said he measured between 12v and 25v between handrail and concrete and water which I believe could have been higher with the right circumstances. Seems like this was a case where bonding created a very dangerous situation. I corrected the problem by re-feeding sub-panel with #8 copper in 3/4" pvc with #10 ground in 120' trench.
When the 2 pole breaker for pool pump was closed voltage was feeding through motor to the cut hot leg and grounding conductor, which was energizing everything that was bonded. Pool guy said he measured between 12v and 25v between handrail and concrete and water which I believe could have been higher with the right circumstances. Seems like this was a case where bonding created a very dangerous situation. I corrected the problem by re-feeding sub-panel with #8 copper in 3/4" pvc with #10 ground in 120' trench.