I know there is a post about this table, but my question is a little different. Now correct me if I am wrong, but when using this table specifically for multiple appliances, you are suppose to add up the results together to get the total kW..no?
For example:
One 8kW and Two 6kW.
1 x 8 = 8 x 0.80 = 6.4
2 x 6 = 12 x 0.65 = 7.8
7.8 + 6.4 = 14.2
Number of appliances for 3 in Column C is 14.
I got a total of 14.2, but being that I am suppose to go for the lowest number for demand load, according to Column C..it is 14 for Three appliances. But I was told 14 is incorrect. Im confused. I also read the Notes, specifically Note 3 since that seems to be the only one that applies.