NEC 250.122(B) requires that when I increase my current-carrying wire size to accomodate long distance voltage drops, that I must also upsize the ground wire proportionally in metal cross sectional area. I like to think in kcmils for this task.
For my examples, all wires are copper with 90C insulation and 75C terminals.
I understand it for single conductor per phase feeds. As a simple example, consider a 64A load on an 80A breaker that would normally have #4 wire, #8 ground, for local cases. Upsize the wire to #2 for voltage drop, and the proportional increase (160%) yields #6 Cu for ground.
What happens when your situation is on the cusp of either paralleling vs not paralling, and voltage drop causes the decision to parallel? Usually I consider 500 kcmil or 600 kcmil to be the maximum size before thinking about paralleling.
Example: a 400A breaker with a 320A load. Locally, it could have either 600 kcmil, or parallel 3/0, and in either case, a #3 ground per raceway. If a single raceway is shared, it would be parallel 4/0 because of the bundling derate.
Suppose I were upsize the live feeders to parallel 350 kcmil, for voltage drop. At this size of wire, if it is 3-phase AC, I wouldn't even about sharing a raceway. Dedicated raceway each set.
I understand that whatever the ground may be, each raceway must contain a full size. No dividing up the kcmil, as I originally would guess.
If 600 kcmil were considered the default, then I've upsized by a ratio of 7/6. Meaning the upsized ground would be #2.
If parallel 3/0 were considered the default, then I've upsized by a ratio of 2.08. Therefore the ground would be #2/0.
So which strategy is correct?
For my examples, all wires are copper with 90C insulation and 75C terminals.
I understand it for single conductor per phase feeds. As a simple example, consider a 64A load on an 80A breaker that would normally have #4 wire, #8 ground, for local cases. Upsize the wire to #2 for voltage drop, and the proportional increase (160%) yields #6 Cu for ground.
What happens when your situation is on the cusp of either paralleling vs not paralling, and voltage drop causes the decision to parallel? Usually I consider 500 kcmil or 600 kcmil to be the maximum size before thinking about paralleling.
Example: a 400A breaker with a 320A load. Locally, it could have either 600 kcmil, or parallel 3/0, and in either case, a #3 ground per raceway. If a single raceway is shared, it would be parallel 4/0 because of the bundling derate.
Suppose I were upsize the live feeders to parallel 350 kcmil, for voltage drop. At this size of wire, if it is 3-phase AC, I wouldn't even about sharing a raceway. Dedicated raceway each set.
I understand that whatever the ground may be, each raceway must contain a full size. No dividing up the kcmil, as I originally would guess.
If 600 kcmil were considered the default, then I've upsized by a ratio of 7/6. Meaning the upsized ground would be #2.
If parallel 3/0 were considered the default, then I've upsized by a ratio of 2.08. Therefore the ground would be #2/0.
So which strategy is correct?