NOOOOOO ! you bond (neutral/ground) either at case or 1st disco, not both ! 250.30(?)Ok guys here's where the fog comes in. In a service, we only are allowed to bond the neutral, ECG, and GEC once in our service. But in separately derived transformers, we must bond neutral to case in transformer, then again at supply side disconnect. So when I think about a service, it brings me to believe that at the utility, there has to be a bond as well. Not that it matters. It's just my imagination.
250.30 (2011)
....
1) System Bonding Jumper. An unspliced system bonding
jumper shall comply with 250.28(A) through (D). This
connection shall be made at any single point on the separately
derived system from the source to the first system
disconnecting means or overcurrent device, or it shall be
made at the source of a separately derived system that has
no disconnecting means or overcurrent devices, in accordance
with 250.30(A)(1)(a) or (b). The system bonding
jumper shall remain within the enclosure where it origi-
nates. If the source is located outside the building or structure
supplied, a system bonding jumper shall be installed at
the grounding electrode connection in compliance with
250.30(C).
Exception No. 1:.....
Thanks for your help. Supply side bonding jumper threw me off. But I think I understand. I'll reply to this again if I have another question. Thanks againwildleg said:NOOOOOO ! you bond (neutral/ground) either at case or 1st disco, not both ! 250.30(?)
bonds exposed metal parts to ground.Shouldn't this be called the MBJ, and not SSBJ? What's the difference?
Thanks for all the help but still very blurry on the difference between the 2. Before the 2011 edition, SSBJ was referred to as MBJ, correct?wildleg said:bonds exposed metal parts to ground. main bonding jumper is the only one that bonds ungrounded conductor to grounding system.
Wildleg is correct, NEC ends at the Mast/Service entrance, pardon this pic having the canadian code section # on it but it may help clear things up a little for you on how a single phase service works. H1-H2 gives you 220V/240V.
Ok guys here's where the fog comes in. In a service, we only are allowed to bond the neutral, ECG, and GEC once in our service. But in separately derived transformers, we must bond neutral to case in transformer, then again at supply side disconnect. So when I think about a service, it brings me to believe that at the utility, there has to be a bond as well. Not that it matters. It's just my imagination.
OK,.....
ThiMk about it.......
~CS~
This is someone's post off of Holt. Pretty cut and dry. Do you guys agree with this?Sunny 1 said:If the system bonding jumper is at the first disconnect means than the wire from sds is called supply side bonding jumper and shall be sized according to 250.66. If the system bonding jumper is at the sds than the wire from sds to first disconnect means is called an equipment grounding conductor and is sized according to 150.122. Is this a correct analysis? Thanks for replies.
K I should have included this pic too to help explain further. The pole part we generally don't worry about unless we are installing a pad mounted transformer for a large service. Lol![]()
This doesn't happen here Daks
Here the poco xformer is fed Hot & Neutral
The Primary side Neutral is bonded right through to the Secondary Neutral, pole GEC (usually #6 solid) , pole guys , etc
Something we, as NEC or CEC disciples would not normally do
~CS~
well thiMk up a way to 'splain this to Sunny smarty pants....OK,
I'm ThiMking, I'm ThiMking . . .