Does an rcd operate on earth fault only or does it operate on short circuit too.? please help;)
1 - 8 of 8 Posts
Does an rcd operate on earth fault only or does it operate on short circuit too.? please help;)

Wasn't sure what an RCD was so I had to look it up.

Here is what Wikepedia says about them;



http://en.wikipedia.org/wiki/Residual-current_device#searchInput
A residual current device (RCD), or residual current circuit breaker (RCCB), is an electrical wiring device that disconnects a circuit whenever it detects that the electric current is not balanced between the phase ("hot") conductor and the neutral conductor. Such an imbalance is sometimes caused by current leakage through the body of a person who is grounded and accidentally touching the energized part of the circuit. A lethal shock can result from these conditions; RCDs are designed to disconnect quickly enough to mitigate the harm caused by such shocks.
In the United States and Canada, a residual current device is also known as a ground fault circuit interrupter (GFCI), ground fault interrupter (GFI) or an appliance leakage current interrupter (ALCI).

Hope this answers your question:whistling2:
See less See more
RCD earth fault
MCB short circuit and overload
RCBO Earth fault and short circuit and overload

Job done:thumbsup:

....why do you need to know
And 9 times out of ten its a neutral earth fault that will trip the UK RCD's
Which is strange as the technical colleges will tell you that the neutral or return wire is dead and is at zero potential on pme systems,

I have had many a jolt off the neutral and can honestly say without any doubt they bl00dy hurt much more that a phase shock.

Chris
RCD earth fault
MCB short circuit and overload
RCBO Earth fault and short circuit and overload

Job done:thumbsup:

....why do you need to know
It came up in a college project and i couldn't find my notes. THANKS:thumbup:
And 9 times out of ten its a neutral earth fault that will trip the UK RCD's
Which is strange as the technical colleges will tell you that the neutral or return wire is dead and is at zero potential on pme systems,

I have had many a jolt off the neutral and can honestly say without any doubt they bl00dy hurt much more that a phase shock.

Chris
I totally agree with the neutral jolt comment. Thanks for getting back to me:thumbup:
Look at this. current is current if it does not pass through the sensor and exceeds the trip set point the GFP/RCD trips.