First thing that comes to mind is that you have a ground (earth) fault between the Main and the Branch.MS Lady said:In my Electrical Installation, the Main RCD (300mA) trips before the second RCD (30mA). This has been happening in various occasions. Does anyone know why this is happening? As far as I know, it should have been the other way round.
Is it possible the ground fault is detected by both is above 300ma and the unlatching time on the 30ma rcd is not fast enough to provide coordination.In my Electrical Installation, the Main RCD (300mA) trips before the second RCD (30mA). This has been happening in various occasions. Does anyone know why this is happening? As far as I know, it should have been the other way round.
If both breakers are tripping at various times, I think it's safe to say that she has a ground fault issue and changing out breakers would be a waste of time and money. I would look first for a specific load that's on when it trips and then work backwards from thereSimply change out the branch circuit RCD breaker, I'll bet that solves it.
Not sure of your brand, but when I returned from Iraq, I had a stack of papers showing real and counterfeit breakers. There were almost as many counterfits as real ones, we knew it , and they were sometimes installed because that was all that was available. Some functioned equally as well as the real deal, though all bets are off as to their long term safety
That is not to say a conterfeit is at fault, but changing out a breaker is cheap. If that doesn't do it, change out the main breaker.