even if it is not a violation I would not accept it.
If it is not a violation you have to accept it right?No
face up??? even if it is not a violation I would not accept it.
Why? There isn't anything wrong with it...code wise.you should submit this to EC&M magazine illustrated catastrophes ,
you may get a prize
http://ecmweb.com/nec/illustrated-catastrophes
Shouldn't it already be gfci protected? Its a commercial kitchen. 210.8?Next72969 said:Lol. Gfi it
110.12 all the way. No professional would do this ****, well....Why? There isn't anything wrong with it...code wise.
Not Approved! (See Definition) And .... "Receptacles mounted to and supported by a cover shall be held rigidly against the cover by more than one screw or shall be a device assembly or box cover listed and identified for securing by a single screw."110.12 all the way. No professional would do this ****, well....
And your avatar is a little to the left.It looks like the previous electrician did a hack job. The receptacle is off center with the drain.
From the NFPAs manual of style.110.12 all the way. No professional would do this ****, well....
The bottom of a cabinet is not a work surface.New in Article 406 in the 2014 NEC
"Receptacles in Countertops and Similar Work Surfaces.
Receptacles, unless listed as receptacle assemblies for countertop applications, shall not be installed in a face-up position in countertops or similar work surfaces. Where receptacle assemblies for countertop applications are required to provide ground-fault circuit-interrupter protection for personnel in accordance with 210.8, such assemblies shall be permitted to be listed as GFCI receptacle assemblies for countertop applications."