New in 2014 NEC

New in Article 406 in the 2014 NEC

"Receptacles in Countertops and Similar Work Surfaces.

Receptacles, unless listed as receptacle assemblies for countertop applications, shall not be installed in a face-up position in countertops or similar work surfaces. Where receptacle assemblies for countertop applications are required to provide ground-fault circuit-interrupter protection for personnel in accordance with 210.8, such assemblies shall be permitted to be listed as GFCI receptacle assemblies for countertop applications."

PS: I just got a copy of the new 2014 NEC handbook as a PDF file; works great searching and copy are allowed.:thumbup:
 

·
Salty Member
Joined
·
31,081 Posts
New in Article 406 in the 2014 NEC

"Receptacles in Countertops and Similar Work Surfaces.

Receptacles, unless listed as receptacle assemblies for countertop applications, shall not be installed in a face-up position in countertops or similar work surfaces. Where receptacle assemblies for countertop applications are required to provide ground-fault circuit-interrupter protection for personnel in accordance with 210.8, such assemblies shall be permitted to be listed as GFCI receptacle assemblies for countertop applications."
The bottom of a cabinet is not a work surface.
 

·
Retired Account
Joined
·
39,697 Posts
As the install may be pre-406, perhaps the answer is rating/listing of the raised 4 sq cvr being installed in the position it is....i.e.- a floor rated cover would be required.......~CS~
 