if your gut is telling you it needs gfci protection, install one and stop worrying about it

what are they? like $12?

if that kills your bottom line, you have more serious problems
It has nothing to do with cost.. just want to use what is needed..
 

·
I own stock in FotoMat!
Joined
·
39,115 Posts
I'm pretty sure, based on memory, you can install a recep in a bathroom within 0.0000000000000000000000000000000001" of the tub.

If this is for a rough inspection, then line-load protect it off the GFCI you're gonna install somewhere in the bath.
 

·
RIP 1959-2015
Joined
·
39,618 Posts
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel. Ground-fault circuit-interrupter protection for personnel shall be provided as required in 210.8(A) through (D). The ground-fault circuit-interrupter shall be installed in a readily accessible location.
Informational Note:  See 215.9 for ground-fault circuit-interrupter protection for personnel on feeders.
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in 210.8(A)(1) through (10) shall have ground-fault circuit-interrupter protection for personnel.
(1) 
Bathrooms



.
 