Discussion Starter · #1 ·
Hi,
if I changed an ungrounded receptacle that in installed in a backbox that has no grd wire, no equipm. grndg with a GFCI type that has no LED indicator , would it be qualified as alternat. for grounded recept.?????

Thank you
 

·
Administrator
Retired EC
Joined
·
24,440 Posts
Tamas you really need to use the correct terminology. A grounded conductor is a neutral and a grounding conductor is the equipment ground.
 

·
RIP 1959-2015
Joined
·
39,618 Posts
Hi,
if I changed an ungrounded receptacle that in installed in a backbox that has no grd wire, no equipm. grndg with a GFCI type that has no LED indicator , would it be qualified as alternat. for grounded recept.?????

Thank you
You're welcome....http://www.nfpa.org/codes-and-standards/document-information-pages?mode=code&code=70

406.4(D)(2)...

(2) Non–Grounding-Type Receptacles. Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(2)(a), (D)(2)(b), or (D)(2)(c).
(a) 
A non–grounding-type receptacle(s) shall be permitted to be replaced with another non–grounding-type receptacle(s).
(b) 
A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.
(c) 
A non–grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked “GFCI Protected” and “No Equipment Ground.” An equipment grounding conductor shall not be connected between the grounding-type receptacles.

(3) Ground-Fault Circuit Interrupters. Ground-fault circuit-interrupter protected receptacles shall be provided where replacements are made at receptacle outlets that are required to be so protected elsewhere in this Code.

Exception:  Where replacement of the receptacle type is impracticable, such as where the outlet box size will not permit the installation of the GFCI receptacle, the receptacle shall be permitted to be replaced with a new receptacle of the existing type, where GFCI protection is provided and the receptacle is marked “GFCI protected” and “no equipment ground,” in accordance with 406.4(D)(2) (a), (b), or (c).
 

·
Premium Member
Licensed Electrical Contractor
Joined
·
11,794 Posts
Don't forget to put the sticker on the GFCI receptacle that says " No Equipment ground."
I've been called on that and had to go back just for the sticker.
What sticker???
I have installed hundreds and hundreds of Cooper and Leviton GFIs. Not once have I seen these stickers in the box.
 

·
Registered
Joined
·
68 Posts
Discussion Starter · #12 ·
You're welcome....http://www.nfpa.org/codes-and-standards/document-information-pages?mode=code&code=70

406.4(D)(2)...

(2) Non–Grounding-Type Receptacles. Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(2)(a), (D)(2)(b), or (D)(2)(c).
(a) 
A non–grounding-type receptacle(s) shall be permitted to be replaced with another non–grounding-type receptacle(s).
(b) 
A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.
(c) 
A non–grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked “GFCI Protected” and “No Equipment Ground.” An equipment grounding conductor shall not be connected between the grounding-type receptacles.

(3) Ground-Fault Circuit Interrupters. Ground-fault circuit-interrupter protected receptacles shall be provided where replacements are made at receptacle outlets that are required to be so protected elsewhere in this Code.

Exception:  Where replacement of the receptacle type is impracticable, such as where the outlet box size will not permit the installation of the GFCI receptacle, the receptacle shall be permitted to be replaced with a new receptacle of the existing type, where GFCI protection is provided and the receptacle is marked “GFCI protected” and “no equipment ground,” in accordance with 406.4(D)(2) (a), (b), or (c).

Good, thanx
 