Why is that? I only use #4 copper stranded myself.I use #2 aluminum for 200A services. Never use copper.
You clearly hate profit.Why is that? I only use #4 copper stranded myself.
Hack saves money anywhere he can. We also use #4 copper.Why is that? I only use #4 copper stranded myself.
He can only use that inside to the water main. Most of us just carry #4 CU on the truck and call it good. Besides, customer pays.Why is that? I only use #4 copper stranded myself.
I don't consider it saving money as much as I see it as not doing something completely unnecessary for no reason at all.Hack saves money anywhere he can. We also use #4 copper.
Inspector is correct.The metal pipe is metal underground from stub continuously to outside where it connects with the city supply. The inspector did not cite code references. He did not mention if he wanted it bonded for grounding electrode purposes or that it was likly to become energized. In Seattle they are no longer giving contractors hand written corrections
Sorry if I missed this, but where are you getting your system ground from?The metal pipe is metal underground from stub continuously to outside where it connects with the city supply. The inspector did not cite code references. He did not mention if he wanted it bonded for grounding electrode purposes or that it was likly to become energized. In Seattle they are no longer giving contractors hand written corrections
You need to do it. I believe it's 250.104.The metal pipe is metal underground from stub continuously to outside where it connects with the city supply. The inspector did not cite code references. He did not mention if he wanted it bonded for grounding electrode purposes or that it was likly to become energized. In Seattle they are no longer giving contractors hand written corrections
Then 250.52(a)(1) Metal Underground Water Pipe does apply and it is considered an electrode conductor.The metal pipe is metal underground from stub continuously to outside where it connects with the city supply. The inspector did not cite code references. He did not mention if he wanted it bonded for grounding electrode purposes or that it was likly to become energized. In Seattle they are no longer giving contractors hand written corrections
There are 2 ground rods and the gas line is also bonded. The electrical panel and grounding system were existing.Sorry if I missed this, but where are you getting your system ground from?
I always get it from the city water pipe, when there is one.
P&L
In that case, I'll stick with post #3.There are 2 ground rods and the gas line is also bonded. The electrical panel and grounding system were existing.