(A) At the dispenser. You must install a listed raceway seal in each conduit run entering or leaving a dispenser. This seal has to be the first fitting after the conduit emerges from the earth or concrete (See Figure 6 ec514-06 514-09A).
(B) At the boundary. You must install a listed raceway seal in each conduit run that leaves a Class I, Division 1 or 2 location. [501.5(A)(4) or 501.5(B)(2)] You can’t use any unions, couplings, boxes or fittings (except explosionproof reducers) between the seal fitting and the point where the conduit leaves the Class I area (See Figure 7 ec514-07 514-09B 01).
[501.5(C)] The raceway seal must be accessible, and cannot contain splices. The total conductor area cannot exceed 25 percent of the cross-sectional area of rigid metal conduit, unless the seal fitting is approved for 40 percent fill (See Figure 8 ec514-08 514-09B 02 501-05C6).
Disconnects and controls
[514.11 ] Disconnects for dispensing stations need to allow for rapid response to a hose breakage or other event that creates a fuel-related fire or explosion hazard:
(A) Each circuit leading to or through a dispenser (including equipment for remote pumping systems) must have a clearly identified and readily accessible switch (located remote from the dispenser) to disconnect simultaneously all conductors of the circuit (including the grounded neutral conductor). You can’t use single-pole breakers with handle ties.
(B) Attended self-service stations must have the dispenser disconnect located no more than 100 ft from the dispenser, at a location acceptable to the AHJ.
(C) Unattended self-service stations must have the dispenser disconnect located more than 20 ft, but less than 100 ft, from the dispensers at a location acceptable to the AHJ. You must install additional emergency controls on each group of dispensers or the outdoor equipment used to control the dispensers to shut off all power to all dispensing equipment at the station.
[514.13] Remote pump control wiring for dispensers must be isolated to prevent electrical feedback. This means dispenser pump control wiring cannot supply more than one dispenser. Otherwise, it could cause electrical feedback when another dispenser is in operation (See Figure 9 ec514-09 514-13 cc514-02).