A customer of mine had squirrels tear up some NM cables in his attic. I suggested a thorough inspection be done (visual) by coming back and clearing insulation to see all cables and also perform a cable insulation test. Anything I'm missing?
I'm also wondering if the megger would read a cable like the one pictured as being good if nothing is close enough to arc or jump/read across. .
I've seen wire like that which would megger fine but was very dangerous if it was missed on a visual inspection, and the mouse/rodent landed on the energized wire.
Somehow the rodents gnaw energized romex all the time but very few are killed.
I've had some pictures of squirrels and gnawed romex at a state fair exhibit and one ole gal chewed my butt for giving them a bad rap:laughing:
A megger is definitely a good check, but it's not fool-proof: I've seen cables with bare exposed copper test fine because there was no fault path (similar to the picture you posted).
I think you just gotta spend a bunch of time feeling out every cable.
A meggar may be enough to find the bad cables if they are laying in damp insulation or something like that......something that can create a conductive path. Otherwise,its just going to be lots of visual inspecting.
I'm surprised with all the technology out there that cable manufacturers haven't found a way to put a repellent on the outter jacket, like the insecticide in the spray foam cans.
It's a big problem, mice and squirrels see it on most every reno job I do