I've installed heat trace on interior pipes in the past bit not the roof style, my question is can you extend a the length by connecting two together as long as you don't exceed the amperage rating of the Supply wiring or do you void the UL listing by doing this?
 

· Moderator
Estwing magic
Joined
·
28,213 Posts
Yes you can splice self reg cable. Refer to the manufacturer's design guide regarding maximum run length, circuit breaker sizing, etc.

If it is a factory made cable set, I would say no, but I could be talking out of my butt.
 

· Registered
Joined
·
22 Posts
Discussion Starter · #3 ·
What I looked at was the factory made cable sets and the end of the length was factory sealed. I could cut and splice on an additional length but think I might just be asking for problems
 

· Moderator
Estwing magic
Joined
·
28,213 Posts

· Registered
Joined
·
425 Posts
Tpg392 said:
What I looked at was the factory made cable sets and the end of the length was factory sealed. I could cut and splice on an additional length but think I might just be asking for problems
I install Danfoss Rx, factory ends, I have never tried to splice but obviously Danfoss states that you can't.
I use their layout to calc length and it works out the right length each time.
Personally, I won't extend, could be opening up a can of worms that you may eventually lose on
 