No attic and have to come into the box. So I guess I will thhn it. Yes on the outside wall.
 

·
Registered
Joined
·
11,434 Posts
...halfway down paragraph in 334.15(C) in states about running conduit or tubing for protection on basement wall
 

·
Registered
Joined
·
15 Posts
Discussion Starter #7
So how about if I have thhn 2 blacks, 2 whites, and a green. Then run them in the 3/4 seal tight about 50 ft long on the exterior of the home? With connector and 1900 boxes at each end? Theres nothing wrong with running seal tight 50ft on an exterior wall is there? Rather than pvc?
 

·
Banned
Joined
·
16,981 Posts
So how about if I have thhn 2 blacks, 2 whites, and a green. Then run them in the 3/4 seal tight about 50 ft long on the exterior of the home? With connector and 1900 boxes at each end? Theres nothing wrong with running seal tight 50ft on an exterior wall is there? Rather than pvc?
You could but it would look like trash.
 

·
Registered
Joined
·
3,342 Posts
you are losing me....you are in a basement and you cant find a spot to fish up thru??
 

·
Registered
Joined
·
11,434 Posts
So how about if I have thhn 2 blacks, 2 whites, and a green. Then run them in the 3/4 seal tight about 50 ft long on the exterior of the home? With connector and 1900 boxes at each end? Theres nothing wrong with running seal tight 50ft on an exterior wall is there? Rather than pvc?
thhn is not rated for wet locations, unless dual rated thwn/thhn
 

·
Electrical Contractor
Joined
·
9,327 Posts
thhn is not rated for wet locations, unless dual rated thwn/thhn
Do they still make wire with only a THHN rating? Everything that comes from my supplier is rated for both. 50' of seal
tight on the exterior of a house??? That will look interesting but won't add any value to the house!!!
 

·
Banned
Joined
·
39,722 Posts
I on this job for a homeowner who is selling and has violations. I have to run (2) dedicated circuits for the kitchen and bathroom outlets. My question is that it will be inspected and is it acceptable to run the (2) 12/2 romexs through the basement then to the outside wall into 3/4 seal tight just as a sleeve. No connectors. Just through the seal tight as protection for the cable. About a 75ft run with 3 90 degree bends. So exiting out of the home then entering into the home just as a sleeve?
sleeving UF might be acceptable....~CS~
 

·
Mad Skills
Joined
·
5,803 Posts
.. is it acceptable to run the (2) 12/2 romexs through the basement then to the outside wall ....

... out of the home then entering into the home just as a sleeve?
I have to question your claim of passing the EC test last year [ #1 ]
 