Had a call yesterday for a house with power fluctuations.
Got there and started doing some testing. No matter how small of a load there was one leg dropped to 90 volts or less and the other would spike to over 140 volts.
I know, classic neutral problem.
So, start doing the normal checks. Neutral in panel, neutral in meter, etc.
Overhead service to meterbase and SEU cable to main breaker panel.
All connections are tight so I suspected it was a utility problem. Spoke with the utility technician and he verified he checked all connection on the pole and re tapped connections at the riser.
So, the only thing to do was replace the SE cable.
No place open yesterday had any 4/0 in stock so I had to wait until today to make the repairs.
When I was removing the old SE, the entire jacket was FULL of water.
Had to slit the jacket open so I could cut the cables to remove them. There was so much water released that I was forced to go home and change after I finished the job.
We see very few jobs done in SE around here and from the ones I run across, they are similar to this.
I'm just wondering if this is a common scenario in the NE and if so why is it still an allowed method?
Got there and started doing some testing. No matter how small of a load there was one leg dropped to 90 volts or less and the other would spike to over 140 volts.
I know, classic neutral problem.
So, start doing the normal checks. Neutral in panel, neutral in meter, etc.
Overhead service to meterbase and SEU cable to main breaker panel.
All connections are tight so I suspected it was a utility problem. Spoke with the utility technician and he verified he checked all connection on the pole and re tapped connections at the riser.
So, the only thing to do was replace the SE cable.
No place open yesterday had any 4/0 in stock so I had to wait until today to make the repairs.
When I was removing the old SE, the entire jacket was FULL of water.
Had to slit the jacket open so I could cut the cables to remove them. There was so much water released that I was forced to go home and change after I finished the job.
We see very few jobs done in SE around here and from the ones I run across, they are similar to this.
I'm just wondering if this is a common scenario in the NE and if so why is it still an allowed method?