Was asked a question from another inspector today and I hope I gave him good info.
The electrical contractor seemingly installed 1 awg aluminum SER cable when they were supposed to install 1 awg copper SER. These feeders are for sub-panels in rooms of a motel.
The feeder breakers are 125 amp. This obviously won't fly with #1 aluminum and being that the SER is in insulation the 125 amp breakers wouldn't have worked with copper either.
I told the other inspector that he might suggest 90 amp breakers as long as the calculated load for each sub-panel doen't exceed 85 amps. Ohio is currently on the 2011 NEC.
Any thoughts?
Pete