I think it fits, but what do I know.
What I'm curious about i how big of a heater are you installing that you want/need to undersize the conductors?
Its a three phase 7500 watt 208 volt forced fan heater. #12 AWG got pulled before the heater was changed to 208 volts. Before it was 600 volts. Here is what I come up with:
Amps = 7500 / (1.73 X 208)
Amps = 20.8
Now sizing the circuit breaker:
Rule 62-144(6)(b)
20.8 x 1.25
= 26
Rule 62-114(8) (From the Pocket Reference code book)
if no match exists, round up to the next higher standard rated circuit breaker or fusible switch
Based on that I go with a 30 amp breaker.
Now conductor size:
Rule 62-114(7)(b) (From the Pocket Reference code book)
When using larger than the minimum standard rated circuit breaker or fusible switch: the ampacity of the standard rated overcurrent device x 0.8
So based upon that 30 x 0.8 = 24. Looking at table 2 75 degree column I can used # 12 AWG. Or do I have to go to #10 AWG because it is not a
fixed resistance heating load.