Hello all, hoping to get some input.... Looking at a new office build out. Space in inside existing building. Never had to do Service calculations before, trying to work my way through it. It will have to be submitted for plan review. Square foot of office space=3495 sgft. Existing is a 42 ckt,225 amp 3 phase panel 120/208 fused by a disco at 100a. They came off a 75kvs trans, tapped to (2) 100a disco's. The panel Im looking at using has the following existing loads, (3) 20a recep circuits- number of recepts unknown, (1) 20a s.p. fuel pump-amps unknown, and (2) 20a s.p. over head doors.
Proposed additional load:
1- 30a 2p electric water heater
63- 20a. receptacles (9 per circuit)
2- 20a. garbage disposals
4- 20a. kitchen circuits- each circuit will have (4) 20a recepts
4- 20a. bathroom exhaust fans

I know this.... 63x180=11340va..first 10000+(50% of 1340)=670
Receptacle load=10670 VA
10670/208=52 amps

Can anyone point me in the right direction of where in ART 220 I can find how to calculate the remainder? My hopes are this 100a panel will support the load. Thanks in advance!
1 - 8 of 8 Posts

· animal lover /rat bastard
Joined
·
13,504 Posts
not likely. a noncoincident load would be something like a heating/cooling unit that could only heat or cool, but not both at the same time.
 

· Registered
Joined
·
39 Posts
service calculation help

the appliances dispossal fans ect are determined by the name plate ratingof the appliance not the breaker size . 20 amp recept. circuits would be 1500 va each water heater would be the wattage of the heater . Also keep in mind article 422appliances requires 125 % increase in branch circuit capacity, this would apply to all appliance loads but not the 20 recept. load .
 