When there are 6 electric storage type water heaters does the continuous load apply or the 75% rule apply since there are more than 4? Electric water heaters are not included in Article 220.53
Ax grinder
I would say that an electric water heater is an appliance (See 422.13) or they wouldn't be mentioned in Article 422.
220.53 allows you to apply a demand factor of 75% to the nameplate rating of 4 or more appliances fastened in place.
So in short you can apply the 75% to the 6 water heaters.
Chris
What sort of occupancy are you talking about? I would think that it might make a difference. If we are talking about, say, an apartment building, with one per unit, then I agree that you could use 75%.