I just did one similar to that here and the POCO made me move and raise the meter. Also raise the mast for the 12' they require at the drop, and change the mast to 2-1/2" rigid.I am currently upgrading the service entrance at a 1951 house. The orginal service was 60 amps. The cable from the pole is attached to the eave of the house about 10.5 feet above ground. I am upgrading to a 125 amp service. The Duke Energy technician tells me that if they run new wire from the pole, I will have to put up a riser to get the 12' clearance over the driveway, but if they use the existing wire, which he says is good for 170 amps, it should be grandfathered in and all I will have to do is run a #2 cable from the meter box up to the eave, a distance of about five feet. However, the county code guy says it's not grandfathered and I will have to put up the riser (through the eave and roof) to get the clearance. Does anyone have any experience or comment on this sort of thing? And do you think that
Code 90.2(B)(5) Installations under the exclusive control of an electric utility where such installations
a. Consist of service drops or service laterals, and associated metering
might apply here? 90.2(B) are situations not covered by the NEC
In your case, I wouldn't listen to a lineman, I would ask the POCO's engineer.
Usually what the POCO requires trumps what the NEC says, from the meter up.