I don't care for the way you ran the bonding bridge. How did you terminate the GEC and that bond wire? Under the same lug?

Is that EMT bonded to the GEC?
If you were my AHJ, then I would care.
All kidding aside.
I wish the intersystem bond was closer to the socket. Yes, both are under the same lug. EMT is bonded at the ground clamp.
 

·
Rest In Peace
Joined
·
6,298 Posts
Discussion Starter · #20 ·
Question.

We did not reconnect the ground wires for the cable and phone. House is vacant. No phone or cable services. Can I be red flagged for not reconnecting?

You are not allowed to splice the phone or cable ground. I have worked installing cable, so I know.
 