I don't care for the way you ran the bonding bridge. How did you terminate the GEC and that bond wire? Under the same lug?

Is that EMT bonded to the GEC?
 

·
Rest In Peace
Joined
·
6,298 Posts
Discussion Starter #17
I don't care for the way you ran the bonding bridge. How did you terminate the GEC and that bond wire? Under the same lug?

Is that EMT bonded to the GEC?
If you were my AHJ, then I would care.
All kidding aside.
I wish the intersystem bond was closer to the socket. Yes, both are under the same lug. EMT is bonded at the ground clamp.
 

·
Rest In Peace
Joined
·
6,298 Posts
Discussion Starter #18
Atta boy! None of that SEU crap. Good old steel riser.
I had to run a mast. Current drop was less than the 12' required for over driveways. But we do not use SE. Pipe and wire. I am using more AL for services and feeders now that I got more leeway from the boss.
 

·
Registered
Joined
·
2,923 Posts
I also think you are undersized on the bonding jumper to the bridge.

edit...unless it is larger than it appears in the picture
 

·
Rest In Peace
Joined
·
6,298 Posts
Discussion Starter #20
Question.

We did not reconnect the ground wires for the cable and phone. House is vacant. No phone or cable services. Can I be red flagged for not reconnecting?

You are not allowed to splice the phone or cable ground. I have worked installing cable, so I know.
 