An inverse time it's used for feeder short circuit protection, what size protection is required for the following three phase motors 40hp,52flc,20hp,27flc,10hp,14flc,5HP,7.6flc
 

·
Coffee drinking member
I pretwist and then use wire nuts. Solder pots rule.
Joined
·
13,959 Posts
dynahd98 said:
An inverse time it's used for feeder short circuit protection, what size protection is required for the following three phase motors 40hp,52flc,20hp,27flc,10hp,14flc,5HP,7.6flc
How about you tell us and show how you came to the answer.
This is homework right.
 

·
Registered
Joined
·
6,189 Posts
I went to trade school with a kid that had a HD superglide. Weird.

I would flip open my code book, go to the index, go to motors, then short circuit protection. If I remember correctly there is a chart based on the type of OCPD that shows you what percentages you can use to calculate feeder OCPD sizing.
 