1 - 13 of 13 Posts
Are the water lines bonded? Could very well have current flowing somewhere. What are they touching when they get shocked? Test for voltage and then turn breakers off until you find the culprit.
Ask about work done in the near past in any of the apartments!?
Yep. I had this same scenario in a four plex. the home run's first stop was in the bathroom light box with a switch loop. Someone (Maintainence) changed out the light and did not connect the neutral from the panel back into the bundle. The circuit still worked, current was returning thru pipes. (old construction, steel boxes, neutrals done up with buchanons without insulation:eek:)
I've told this service story on here already but I had a lady that was getting juiced off her bathroom sink. So we spent a bunch of time troubleshooting and re- grounding her house and one day we were out their and I had a revelation and it was her water heater element. So I told her and she called a tech out and we never got a call back from her.
Retired Account
Had the same problem, 3-5v on tub & sink hardware
The usual shtick is to turn off one breaker @ a time until the culprit is outed
But that didn't happen.....:( , only removing the GEC from the municipal h20 made it go away (yes the ser ent noodle was the very next thing we checked)
So we bonded the holy h-e-double hockey sticks outta everything anyways.
We could not get a reading after that, but i believe we simply provided an equopotential instead of eradicating what still is a whole house noodle
Checked an apt complex with 2 apts tenants report shocked in shower and at kitchen sink
Well, turn off your computer and go find the source and fix it before someone gets hurt.
I'd start with POCO neutral connection. If it is compromised or open, current may be flowing through the bonded piping.
Apt complex? Do the 2 units share a service?
I've seen it 4 times from 4 different reasons. Once in my own home :laughing:
1 - 13 of 13 Posts