My company recently acquired some new facilities. When I went to check one of the 69Kv - 34.5 KV power stations, at the new facilities, I noted that the neutral wire, of the solidly-grounded 34.5Kv system, was routed from the transformer XO bushing down the exterior of the transformer through a 1 inch rigid metal conduit, for approximately 25 feet in length, attaching to the ground grid of the substation. I am curious as to the induction effects of the wire in the ferrous conduit during a heavy fault.
We have had two 34.5Kv, KYLE (Cooper Power Systems) type WVE38X reclosers to fail in the last four months. They have failed internally and the resultant arcing pressurized the tank and hot/flaming oil spewed out the tank gasket/O-ring upward and outward for approximately 30 feet. We dropped the tanks and found in both cases the 34.5Kv closing coil circuitry had failed with resulting arcing from phase A to the tank and the internal framework...it was also noted that a heavy flashover had occurred between the external bushing of phase B and phase C on the source side of both reclosers. There are no surge arresters on either the source side or load side of the reclosers.
I am curious as to the effective high impedance, of the neutral wire in the conduit, possibly created during a heavy fault limiting fault current and shifting the effective neutral point and creating high voltages on the phases that are not grounded. Has anyone encountered this scenario? Do you recommend the changing of the rigid metal conduit to nonmetallic rigid conduit or is the induced effect possibly minor to non-existent?
We have had two 34.5Kv, KYLE (Cooper Power Systems) type WVE38X reclosers to fail in the last four months. They have failed internally and the resultant arcing pressurized the tank and hot/flaming oil spewed out the tank gasket/O-ring upward and outward for approximately 30 feet. We dropped the tanks and found in both cases the 34.5Kv closing coil circuitry had failed with resulting arcing from phase A to the tank and the internal framework...it was also noted that a heavy flashover had occurred between the external bushing of phase B and phase C on the source side of both reclosers. There are no surge arresters on either the source side or load side of the reclosers.
I am curious as to the effective high impedance, of the neutral wire in the conduit, possibly created during a heavy fault limiting fault current and shifting the effective neutral point and creating high voltages on the phases that are not grounded. Has anyone encountered this scenario? Do you recommend the changing of the rigid metal conduit to nonmetallic rigid conduit or is the induced effect possibly minor to non-existent?