I sometimes encounter "single-plex" receptacles in garages of newer houses.
Does this have something to do with 210.21(B)(1)
Does it have something to do with dedicated laundry circuits? Though I do not recall seeing plumbing adjacent to these outlets.

210.21(B)(1) Single Receptacle on an Individual Branch Circuit.
A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.

I also saw this on a Mike Holt forum but I think the article number is wrong:
Receptacles. You can use 15A or 20A receptacles on 20A circuits as long as there is more than one receptacle on the circuit. For these purposes, a duplex receptacle is considered to be two receptacles [210.21(B)(3)].
 

· Registered
Joined
·
3,106 Posts
I sometimes encounter "single-plex" receptacles in garages of newer houses.
Does this have something to do with 210.21(B)(1)
Does it have something to do with dedicated laundry circuits? Though I do not recall seeing plumbing adjacent to these outlets.

210.21(B)(1) Single Receptacle on an Individual Branch Circuit.
A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.

I also saw this on a Mike Holt forum but I think the article number is wrong:
Receptacles. You can use 15A or 20A receptacles on 20A circuits as long as there is more than one receptacle on the circuit. For these purposes, a duplex receptacle is considered to be two receptacles [210.21(B)(3)].
A single receptacle installed on an individual branch circuit must have an ampere rating not less than that of the branch circuit. For example, a single receptacle on a 20-ampere individual branch circuit must be rated at 20 amperes in accordance with 210.21(B)(1); however, two or more 15-ampere single receptacles or a 15-ampere duplex receptacle are permitted on a 20-ampere branch circuit in accordance with 210.21(B)(3).
 

· Registered
Joined
·
2,923 Posts
From the 05

Exception 1

Receptacles that are not readily accessible.

Exception 2

A single recept or a duplex recept for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-plug connected.

These exceptions specifically for garages and basements.
 

· Premium Member
Licensed Electrical Contractor
Joined
·
11,733 Posts
A general contractor once told me something about the GFI exception. I couldn't find anything to back up his claim.
Depends on what you consider a "newer" house.
I take this as something only a few years old.
The exception was last in the 2005 NEC as Deep quoted.
 