Discussion Starter · #1 ·
Need to know wat size of main breaker I need for a sub panel in a tool shed. there is a shed wit a fuse box that's existing but im moving the shed and tearing the old one down. that fuse box is fed from the main panel in the house and comes from a 50 A breaker wich is fine for wat will be needed for the new shed. any help be appreciated if u need more info just ask. thank you.
 

· fertilizer distrubuter
Joined
·
1,247 Posts
Run two 8 hots a 6 neutral and a 10 ground in pvc conduit. The breaker size on the sub panel does not matter as long as it is greater than 50A. You don't need a main breaker panel at all as long as there are less than 6 branch circuits and feeders from the sub panel. It does need a ground rod and main bonding jumper.
 

· Registered
Joined
·
259 Posts
Ultrafault said:
Run two 8 hots a 6 neutral and a 10 ground in pvc conduit. The breaker size on the sub panel does not matter as long as it is greater than 50A. You don't need a main breaker panel at all as long as there are less than 6 branch circuits and feeders from the sub panel. It does need a ground rod and main bonding jumper.
Main bonding jumper???
 

· Administrator
Retired EC
Joined
·
24,993 Posts
Run two 8 hots a 6 neutral and a 10 ground in pvc conduit. The breaker size on the sub panel does not matter as long as it is greater than 50A. You don't need a main breaker panel at all as long as there are less than 6 branch circuits and feeders from the sub panel. It does need a ground rod and main bonding jumper.
I have never been caught on it but if you check you will see that most ML panels will not be compliant if you don't use a main breaker kit. In most cases I use the kit not 6 discos especially now that I know it is not compliant. 225.36 is the art. and the instructions in the panel say that the ML panel is listed for service equipment when a main breaker kit is installed.

The 2014 does away with this except when we use an existing feeder that does not have an equipment grounding conductor.
 

· Registered
Joined
·
189 Posts
Need to know wat size of main breaker I need for a sub panel in a tool shed. there is a shed wit a fuse box that's existing but im moving the shed and tearing the old one down. that fuse box is fed from the main panel in the house and comes from a 50 A breaker wich is fine for wat will be needed for the new shed. any help be appreciated if u need more info just ask. thank you.
well how many sheds do you have there?
 