Are you referring to 210.19(3) Exception No. 1You might be allowed to use the tap rule and eliminate the panel and just straight tap both appliances from said circuit. I have only done it twice in 20 years. I believe it is still compliant with some requirements.
Yes.Are you referring to 210.19(3) Exception No. 1
Conductors tapped from a 50A branch circuit supplying electric ranges, wall-mounted electric ovens, and counter-mounted electric cooking units shall have an ampacity of not less than 20A....
Thanks for pointing that out Dennis.Swimmer have you looked at the capacity of 8/3 nm?
Yes, and they are built exactly for this situation. Just explain to the parts guy you need one of these tiny little junction boxes made for it, and he'll know exactly what you need. They're tiny! And it's the way to go! Remember it has to be accessable.Does anyone know of such a panel?
Thanks
He needs a breaker panel not a j box you ding-dong. :laughing::laughing:Yes, and they are built exactly for this situation. Just explain to the parts guy you need one of these tiny little junction boxes made for it, and he'll know exactly what you need. They're tiny! And it's the way to go! Remember it has to be accessable.
Whatever, it looks like a junction box but it has breakers in it.He needs a breaker panel not a j box you ding-dong. :laughing::laughing:![]()
Don't take the troll bait.He needs a breaker panel not a j box you ding-dong. :laughing::laughing:![]()
Too late...Don't take the troll bait.
He's replacing this 50A unit with a 30A range and a 20A oven (or something to that effect) so he'd like to put a 50A sub-panel under the appliances to avoid tearing up drywall. So the 8/3 romex remains in place and then I'll run flex conduit from the box to the sub-panel and wire the appliances into this panel.
The available space for this panel is only 6" high.
So I need a panel with 4 spaces that is 6" high or less.
The smallest residential panels I can find are 13" high.
Width and depth are not a concern.
Does anyone know of such a panel?
Thanks
Shut up, troll.Peter you're following me around like some queer. Stop it.
I'm looking for a pic. It's for when you have a regular oven, and you're replacing it with an oven/cooktop that's split requiring different power sources.
Could be the USA doesn't have them. Or maybe you guys are just ignorant.