We are about to start wiring a single family home that was a total loss due to fire.
Homeowner has hired a company to install a fire alarm system throughout home including smoke detectors. This company has told homeowner that they install all smoke detectors and the electricians are not to install any.

I have had this in the past and our local inspector still required us to install all our smoke detectors as we are normally require to.

Seems silly to have double the amount of smoke detectors in the house than they need.

What are your guys thoughts on this ?
Maybe a code reference ?

Thanks guys
 

·
animal lover /rat bastard
Joined
·
13,547 Posts
I went round and round with this on my own damn house no less. just ask your inspector what they require. I would still rough in the smokes and blank em off for future, but that's just me.
 
  • Like
Reactions: Dolson226

·
Administrator
Retired EC
Joined
·
24,053 Posts
Around here if it is a listed system and they install the smokes and carbons to code then there is no need to install our units.
 

·
Registered
Joined
·
9,204 Posts
Unless you can clarify from an inspector to do otherwise, install yours. It is likely the alarm company's system will one day become completely defunct when the HO gets tired of shelling out monthly monitoring fees.
 

·
Registered
Joined
·
830 Posts
IslandGuy said:
Unless you can clarify from an inspector to do otherwise, install yours. It is likely the alarm company's system will one day become completely defunct when the HO gets tired of shelling out monthly monitoring fees.
This is what our inspector says and usually requires hard wired units as well.
 

·
Registered
Joined
·
16 Posts
Discussion Starter · #6 ·
IslandGuy said:
Unless you can clarify from an inspector to do otherwise, install yours. It is likely the alarm company's system will one day become completely defunct when the HO gets tired of shelling out monthly monitoring fees.
That was my thought exactly. I'm not real familiar with the fire alarm systems. I was wondering if HO was did stop paying for the services would the system still work like ours would. I imagine it would but not for sure.

Thoughts ?
 

·
Electrical Contractor
Trying to retire or at least slow down a bit, but life not cooperating
Joined
·
5,246 Posts
Unless you can clarify from an inspector to do otherwise, install yours. It is likely the alarm company's system will one day become completely defunct when the HO gets tired of shelling out monthly monitoring fees.
This is what our inspector says and usually requires hard wired units as well.
Exactly the same reasoning here.
In the future, the HO decides the alarm system is PITA, so the thing gets turned off. Or lack of maintenance and the system doesn't work properly.
 
  • Like
Reactions: Dolson226

·
Registered
Joined
·
196 Posts
It's not a problem here to let the alarm co take care if the smokes, as long as they're installed to code, every bedroom and hallway. However, I've only had one instance where the alarm co also did the COs.
On new jobs, I try to convince the customer to use the alarm system for smokes. A chirping smoke detector is my least favorite service call.
 

·
Registered
Joined
·
16 Posts
Discussion Starter · #11 ·
Thank you all for your responses. I have a call in the the local inspector just waiting for the call back, and wanted some other opinions & experiences
 

·
Conservitum Americum
Joined
·
8,927 Posts
Exactly the same reasoning here.
In the future, the HO decides the alarm system is PITA, so the thing gets turned off. Or lack of maintenance and the system doesn't work properly.
We are in a "dialog" defined ,argument, with our AHJ. We were asked to put two horn strobes and a pull station in a small café which already has a functional sprinkler system. We did so. We also tied in the sprinkler and the Ansul cooking hood extinguisher system in for notification.

Now you know the sprinkled building does not require a fire alarm per se. BUT, since we did install the notification appliances, the AHJ says he wants us to "bring it up to code" by installing horn strobes in the bathrooms. We contend the code has already been met and we went beyond our obligations to comply with code as a fire alarm installing company as there really was no requirement to install any fire alarm in this sprinkled building.

The problem here is the design of the building. In order to do so we would have to pipe it in behind existing walls and 20 ft to the rediron. Other trades would also be called back in to repair what we tear up in order to accomplish this nonrequired install.

Is "Because I said so." really a valid reason to charge the owner around $5,000 for two horn strobes?
 

·
Electrical Contractor
Trying to retire or at least slow down a bit, but life not cooperating
Joined
·
5,246 Posts
As opposed to magical 120v systems that require no maintenance and can't be turned off. :laughing:
Which is why in the CEC, smoke alarms are tied in with the lighting circuit.

The point is that an intrusion alarm system is not essential in a house and if turned off, would remove the safety coverage .
 

·
Electrical Simpleton
Joined
·
3,350 Posts
Which is why in the CEC, smoke alarms are tied in with the lighting circuit.

The point is that an intrusion alarm system is not essential in a house and if turned off, would remove the safety coverage .
What would stop the HO from removing the smokes and blanking them off?

Neither system (single station detectors) or a fire alarm system is 100% fool-proof to an adequately armed fool.

The ORC (Ohio Residential Code) would accept either. My preference would be single station detectors but I can't enforce my opinion.

Pete
 

·
Retired Account
Joined
·
39,697 Posts
My state has a huge focus on smoke detection, and rightly so given all the construction debaucheries good detection makes lesser sins of


~CS~
 

·
Registered
Joined
·
9,204 Posts
That was my thought exactly. I'm not real familiar with the fire alarm systems. I was wondering if HO was did stop paying for the services would the system still work like ours would. I imagine it would but not for sure.

Thoughts ?
That would depend on the system. Many are installed "free" or at a discount with the proviso that the HO enter a 2 year monitoring agreement. No agreement, no system, and definately no technical support or replacement components, hence the need for the code required hardwired units.
 

·
Registered
Joined
·
9,204 Posts
As opposed to magical 120v systems that require no maintenance and can't be turned off. :laughing:
There's maintenance and then there's maintenance. Installing a fresh battery in a hardwired detector is as easy as a remote control. In addition, a hardwired system will not have a horn inside and outside every bedroom and in each hallway. It is likely one could sleep through an alarm system's horn when you're in the 1st floor bedroom and the horn is in the attic, facing the street.
 

·
Registered
Joined
·
9,204 Posts
We are in a "dialog" defined ,argument, with our AHJ. We were asked to put two horn strobes and a pull station in a small café which already has a functional sprinkler system. We did so. We also tied in the sprinkler and the Ansul cooking hood extinguisher system in for notification.

Now you know the sprinkled building does not require a fire alarm per se. BUT, since we did install the notification appliances, the AHJ says he wants us to "bring it up to code" by installing horn strobes in the bathrooms. We contend the code has already been met and we went beyond our obligations to comply with code as a fire alarm installing company as there really was no requirement to install any fire alarm in this sprinkled building.

The problem here is the design of the building. In order to do so we would have to pipe it in behind existing walls and 20 ft to the rediron. Other trades would also be called back in to repair what we tear up in order to accomplish this nonrequired install.

Is "Because I said so." really a valid reason to charge the owner around $5,000 for two horn strobes?
"Because I said so" isn't a valid reason, whether the additional work costs $50.00 or $50,000.00. If you are right and the inspector is wrong, it's time to prove your case, and go over his head if needs be.
 

·
Registered
Joined
·
23 Posts
We are in a "dialog" defined ,argument, with our AHJ. We were asked to put two horn strobes and a pull station in a small café which already has a functional sprinkler system. We did so. We also tied in the sprinkler and the Ansul cooking hood extinguisher system in for notification.

Now you know the sprinkled building does not require a fire alarm per se. BUT, since we did install the notification appliances, the AHJ says he wants us to "bring it up to code" by installing horn strobes in the bathrooms. We contend the code has already been met and we went beyond our obligations to comply with code as a fire alarm installing company as there really was no requirement to install any fire alarm in this sprinkled building.

The problem here is the design of the building. In order to do so we would have to pipe it in behind existing walls and 20 ft to the rediron. Other trades would also be called back in to repair what we tear up in order to accomplish this nonrequired install.

Is "Because I said so." really a valid reason to charge the owner around $5,000 for two horn strobes?
It never stops amazing me how different areas have exactly opposide ideas on what should be code. Around here if a building has a sprinkler system, not only does it require a F/A system but that system is to be monitored so fire department gets call if alarm is activated. I guess they do not want water flowing and no one showing up (makes sense to me).
 