Electrician Talk banner
1 - 1 of 5 Posts

· Swimmer
Joined
·
701 Posts
Discussion Starter · #1 · (Edited)
I have a full Siemens 3-phase panel in a Deli where I'd like to add a circuit. There are 1-pole, 2-pole and 3-pole breakers in this panel.

The panel is fed by 120 / 208

This line used to say I could use 220V or 115V. That was wrong. I need to provide both.

I have never seen space saver breakers in commercial applications.
Is there a reason for this?

Do they make 1 or 2 pole space savers for these types of panels?
 
1 - 1 of 5 Posts
This is an older thread, you may not receive a response, and could be reviving an old thread. Please consider creating a new thread.
Top