· Super Moderator
Florida, USA
Joined
·
9,346 Posts
For a different reason I agree you should stand back and observe. You represent the owner. You watching means you'll know exactly how it's there when the time comes years from now to address it again, due to more settling. EC is paid to do the work so let him earn his revenue.
 

· Chief Flunky
Field Service Engineer
Joined
·
4,193 Posts
So long story short there are some 600 mcm feeders that due to settling are getting to the point of being to short. I talked with a contractor today about possibly splicing on a short piece to the end to save them. I'm just curious what would be the best option for wire this big. Big hydraulic crimp barrel? Polaris type lugs ? Old school eye barrels and tape? I don't have any knowledge of splicing this big of wire (hence bring in a contractor) but just want to learn what's out there.
I handle large above NEMA motors, starters, and drives all the time. I carry #22 to 500 MCM lugs and tools stock on the truck. I carry terminations to 15 kV too. Customers that know this sometimes just call to buy lugs in emergencies.

Depends on you needs. Hands down Cadwelded terminations/splices are the most permanent. Next to that crimped termination nations are permanent but more or a cold rather than hot weld. Utilities use cadweld underground on ground grids in substations and crimped lugs everywhere else. Some even spec it for control wiring.

Whether to use a bolted pair or lugs or a barrel connector is a function choice: Barrel connectors are cheaper but you can never take them apart: Once you crimp it on removal means cutting off more cable. With lugs you have options. There might be a tiny bit more risk but bolt failures are either lack of proper sizing, not tightened or galled, or bad tape jobs.

Insultaps or Polaris taps work for a while. I have replaced many failed ones. Like any mechanical lug you have a huge working size range but higher failure risk. The crimp stuff is very idiot proof. On my crimper I hold the trigger until it finishes and retracts. On my manual you squeeze until the pressure relief trips. On an Allen head 85% of the torque goes into overcoming thread friction. How do you know how much tension you applies? You don’t. That’s on top of the tendency for aluminum and brass set screws to strip or gall or jam on a thread of wire. Lugs are so much easier.

There can be a Code issue. You aren’t supposed to have joints in the middle of raceways. Strict interpretation means pulling out the old cable. Cadweld really is not a joint. You can argue barrel connectors aren’t either. All others can be taken apart so it’s as legal as using wire nuts in a conduit body.

The splicing decisions are the SAME no matter the size. You just have fewer options at larger sizes. I’m sure Mike will be along any time now to talk about Wago Levernuts but I have not seen a 600 MCM Wago. I have seen that size cam locks and pin connectors but that’s another story.
 

· Registered
Water treatment plant maintenance
Joined
·
1,304 Posts
Discussion Starter · #23 ·
I've worked with this contractor a lot in the past on projects here, so it's not like we are strangers. It's one of those deals where he will take care of certain aspects of the project and I'll take care of certain other aspects of the project. I'll certainly be there to make sure it goes smooth and lend a hand when the need arises.
 

· Chief Flunky
Field Service Engineer
Joined
·
4,193 Posts
So are these things that you crimp on with a big hydraulic crimper? I assume so. Do they sell appropriate insulation sleeves or tape them up with the rubber tape or ?
Yes.

Correct (3M procedure) is two layers of varnished cambric to cover sharp edges but practice is anything really. Cloth, glass, or vinyl tape is often used. Then at least 2 layers of rubber splicing tape. Then 2 layers of vinyl tape.

You can also get heavy wall adhesive lined heat shrink for the ultimate waterproofing. Make sure to slide it on FIRST before crimping. In multiconductor cables stagger the joints. This is good practice anyway. Shrink one on per barrel then one overall (multiconductor only). I often buy the bigger ones from McMaster Carr. Next day delivery. The thing is though I’ve done thousands. Getting everything the right length and shrinking evenly takes a little practice so this is a terrible technique for one off attempts where tape is forgiving…you can always add more or cut it off and redo it. Heat shrink is pretty much once and done.
 

· Hackenschmidt
Joined
·
14,564 Posts
The crimp stuff is very idiot proof. On my crimper I hold the trigger until it finishes and retracts. On my manual you squeeze until the pressure relief trips.
The thing with the manual is it takes two hands and those hands can't be close to the work, so you kind of want a third hand to hold the wire in the connector.
 

· Hackenschmidt
Joined
·
14,564 Posts
Regarding maintenance and contractor working together, for me that depends. I have a number of customers I work side by side with their maintenance people and it works out well all around. Some places they have better things to do than help me. Some places they are just in the way.

A few times I've had management change at a company and for a while and someone gets a bug up their ass about cutting out the outside contractors, and they want to have maintenance "shadow" me at all times so they can learn to do it themselves. I used to get very pissed about this, now I just roll my eyes, it doesn't amount to anything.
 

· Registered
IBEW 6 volts to lightning bolts
Joined
·
1,265 Posts
I do miles of 600’s. Rent a crimper head and a powered hydraulic pump. You can do cold or hot shrink. I use the giant greenlee pump from the 4” table bender. Lighting fast crimps. Watch yer fingers


Sent from my iPhone using Tapatalk
 

· Chief Flunky
Field Service Engineer
Joined
·
4,193 Posts
The thing with the manual is it takes two hands and those hands can't be close to the work, so you kind of want a third hand to hold the wire in the connector.
Never a problem for me. I like to lay the crimper down if I can and insert the lug and better yet wire too but that’s not absolutely necessary. It’s a pretty rare day that I have to crimp in open air. That’s more of a lineman thing. Crimp just until it holds the fitting. Do NOT crush it yet, just enough to hold it. Then I can let go of the crimp and insert/hold the cable into the lug while using the other hand to pump the crimper. After a couple squeezes the wire is not going anywhere. On the rest of the crimps I can just rest the crimper against my hand (not on the die! Frame only) and repeat the procedure until they are all done. Just remember that once the crimper is applying pressure, it’s not going anywhere. Once the cable is being crushed, it’s not going anywhere. Put the first crimp out close to the shoulder. Subsequent crimps move towards the barrel opening. This way everything is held in place the whole time. If you need to you can always do another crimp closer to the lug shoulder but once the first crimp is on, forget ever removing the wire.

Hydraulic crimpers (true hydraulic) are cheap and very fast but the pumps are very expensive. At most we do maybe a hundred lugs in a day so we haven’t been able to justify the bigger tools yet.The slow part of the process stripping and pulling.
 

· Premium Member
Joined
·
20,221 Posts
So long story short there are some 600 mcm feeders that due to settling are getting to the point of being to short. I talked with a contractor today about possibly splicing on a short piece to the end to save them. I'm just curious what would be the best option for wire this big. Big hydraulic crimp barrel? Polaris type lugs ? Old school eye barrels and tape? I don't have any knowledge of splicing this big of wire (hence bring in a contractor) but just want to learn what's out there.
How many splices do you need to make?
I have quite a few Shearbolt Butt Splices and lugs on hand.

Material property Gas Cylinder Metal Auto part

Musical instrument Material property Font Cylinder Metal
 

· Registered
Water treatment plant maintenance
Joined
·
1,304 Posts
Discussion Starter · #34 ·
Those shearbolts look pretty cool, they look like a serious chunk of change though I bet. Which everything this size is. Was quoted 21 bucks a foot for wire today. Right now I'm thinking we will end up doing 24 splices. 2 each on 12 wires to add a loop in the middle. We could unterminate the mcc pull slack back to the box and add on the end with only 1 splice per wire then reterminate in the mcc, but... My thinking is there is a higher risk of failure due to the better chance of damaging the wire trying to wrestle it out and back in and reterminate than the extra splice would ever cause. In the end the contractor will be responsible for the splices, I'm just an observer with a curious mind that always wants to know how other poeple do this work.
 

· Premium Member
Joined
·
20,221 Posts
I would number all of those cables and cut them.
Have 75' of 600 on site and 50 crimps with the adhesive type heat shrink.
Cut 16- 3' pieces of the 600
Give your crew an hour to strip the ends.
Set all of the heat shrink on the cables.
Crimp a butt splice on all of the existing cables.
It will take about 20 minutes to crimp all of the butt splices.
Give your crew an hour to heat shrink the 24 butt splices.

We could do this job in about 3 to 4 hours max.

Pay your crew for the day.
 

· Registered
Water treatment plant maintenance
Joined
·
1,304 Posts
Discussion Starter · #38 ·
So to take this on a little bit of a nerdy detour. I've been researching these crimps trying to wrap my head around it all. It appears that the "U style" is the most popular. I've also ran across a "w style" plus a bunch of proprietary named stuff, as well as some hex shaped stuff etc. I'm assuming the "u style" at least is standardized with standard dimensions etc? I can't find any good tech details on these crimps. Coming from a past in hydraulics etc I'm used to stuff like JIC fitting where everything is standardized and there is technical information out there. Or is it that everyone makes their own lugs and their own dies and gets them listed together just so you have to keep buying from the same company.
 

· Registered
Ready-Mix Electrician
Joined
·
3,999 Posts
Coming from a past in hydraulics etc I'm used to stuff like JIC fitting where everything is standardized and there is technical information out there. Or is it that everyone makes their own lugs and their own dies and gets them listed together just so you have to keep buying from the same company.
There’s more similarities than you realize here. You’re not supposed to crimp an Aeroquip fitting with a Parker crimper are you? We all have though. No manufacturer wants to take the time to make sure that a crimper from Gates will make a proper crimp on a Weatherhead fitting.
It’s pretty much the same in electrical, buy their crimper and their terminals.
 