Splicing large (600 mcm) wire

3858 55
So long story short there are some 600 mcm feeders that due to settling are getting to the point of being to short. I talked with a contractor today about possibly splicing on a short piece to the end to save them. I'm just curious what would be the best option for wire this big. Big hydraulic crimp barrel? Polaris type lugs ? Old school eye barrels and tape? I don't have any knowledge of splicing this big of wire (hence bring in a contractor) but just want to learn what's out there.
41 - 56 of 56 Posts

·
Banned
Commercial/Industrial and Service work
Joined
·
1,822 Posts
I didn’t see the pressure specification in the product info. That’s one if not the the most important criteria that should be listed.


Sent from my iPhone using Tapatalk
12ton
And if you use the one key app you can actually download the force data for each crimp you do
 

·
Registered
Joined
·
308 Posts
On an Allen head 85% of the torque goes into overcoming thread friction. How do you know how much tension you applies? You don’t. That’s on top of the tendency for aluminum and brass set screws to strip or gall or jam on a thread of wire. Lugs are so much easier.
I was a Manufacturing Engineer. Torque specifications do not require that one considers what load is on the threads vs the mechanical force at the connection (which is controlled by the shape and type of contact being made such as with a set screw). Torque values is engineered by the surface finish, inorganic metal finish, and thread pitch and size. If your components are galling at torque spec then you have bad parts. All torque specification applications are designated for minimum of 3 cycles before any consideration of failure of any type such as galling or thread distortion etc (with the exception of lug nuts on vehicle wheels and a few others designed for repeated replacement cycles). Failure in under three cycles means that torque values were exceeded, that the parts were not clean or had contaminants introduced, or that oil or other lubricant was used against specification.
I hope this helps resolve consideration of thread load verses contact load.
 

·
Registered
Ready-Mix Electrician
Joined
·
3,769 Posts
View attachment 160122

If I wanted to get fancy I could pull the bare wire out of some romex and serve up a joint like the bottom picture. Add some solder and rubber tape, that thing ain't going anywhere.
You forgot the layer of friction tape over the rubber tape.
 
41 - 56 of 56 Posts