Wouldn't that duct tape, and string have to be UL listed? :yes:This is the way I understand it:
You can secure or support romex with anything, it doesn't have to be a listed means of support. So you can use tywraps or string or duct tape. When doing that, you have to avoid bundling too many together, which is a whole 'nother issue.
When using an item that is listed for supporting romex, then you have to use that item according to it's listing. So if you use a romex staple and the staple says it can support 2 cables, then that's what it can support. A stacker says it can support 4 romex, a CJ says 6.
Anyone disagree?
What if you use a staple that isn't listed for supporting romex? Does that mean you can staple 4 romexes with it?
Any more than 9 current carrying conductors and you derate. This picture is of a double. I go up to 4 cables with a staple(special staple) then to five I use 3M cable stackers.I don't see in the NEC anything about stapling more than one run of Romex under 1 staple, only distances betweeen and at boxes, etc.
What's the common practice/rule in the field?
Sounds right to me. Of all of the options listed, I'd say staples are my least favorite.This is the way I understand it:
You can secure or support romex with anything, it doesn't have to be a listed means of support. So you can use tywraps or string or duct tape. When doing that, you have to avoid bundling too many together, which is a whole 'nother issue.
When using an item that is listed for supporting romex, then you have to use that item according to it's listing. So if you use a romex staple and the staple says it can support 2 cables, then that's what it can support. A stacker says it can support 4 romex, a CJ says 6.
Anyone disagree?
What if you use a staple that isn't listed for supporting romex? Does that mean you can staple 4 romexes with it?
In my post that you quoted I said this:Wouldn't that duct tape, and string have to be UL listed? :yes:
I also mentioned that I am not completely sure about it all, so if you have a code article saying romex support needs to be listed, please post it.You can secure or support romex with anything, it doesn't have to be a listed means of support.
This is first year apprentice stuff.In my post that you quoted I said this:
I also mentioned that I am not completely sure about it all, so if you have a code article saying romex support needs to be listed, please post it.
I am starting to think you are a real dolt, as telsa would say. You keep posting garbage across multiple threads. What you just posted doesn't apply to this conversation at all.This is first year apprentice stuff.
Article 100 Definitions - "Listed".
110.3 (B) Installation and use.
110.21 (A) Manufacturers marking.
Hope this helps.
That's easy: one or two Romex runs per staple.I don't see in the NEC anything about stapling more than one run of Romex under 1 staple, only distances betweeen and at boxes, etc.
What's the common practice/rule in the field?
I gave you the code sections, they apply to everything, if you can't read, that's not my problem. Maybe you could have someone read it to you.I am starting to think you are a real dolt, as telsa would say. You keep posting garbage across multiple threads. What you just posted doesn't apply to this conversation at all.
I will ask again, show me where code requires romex to be supported with listed material.
Until you provide that, which you won't, we all know that romex does NOT in fact require listed support and can be supported/secured with the items I mentioned.
You are saying that romex is required to be secured with listed items, but you can't cite the listing requirement for it?I gave you the code sections, they apply to everything, if you can't read, that's not my problem. Maybe you could have someone read it to you.
I'm starting to believe you secure your work with duct tape and string.
In fact I have no doubt.
There is no listing requirement. You bring up a completely different topic.334.30 Securing and Supporting
Nonmetallic-sheathed cable shall be supported and secured by staples, cable ties, straps, hangers, or similar fittings designed and installed so as not to damage the cable, at intervals not exceeding 1.4 m (4 1/ 2 ft) and within 300 mm (12 in. or 8" using 314.17(C) Ex. if meets allowance) of every outlet box, junction box, cabinet, or fitting. Flat cables shall not be stapled on edge. Sections of cable protected from physical damage by raceway shall not be required to be secured within the raceway.
If it were my job, I would argue duct tape and string were not designed to be used to support NM. Even if not listed, it implies it needs to be a product designed to support NM in such a way to not damage the cable, and to be installed in that manner as well.
I have seen couple inspectors just bat the eyes and say not much with tiewraps straps for NM's and one did look at me but never say a word as long it is used for support.,,There is no listing requirement. You bring up a completely different topic.
We have known for years that tie wraps have been acceptable to secure romex. Tie wraps aren't designed with any specific link to romex. That alone shows that the design part of it doesn't mean the product has to be made for romex.
Its those cheesy knock offs of the original slim jimWhat are these Colorado Jim things you guys are talking about? Am I on the wrong forum again?...
I was about to answer you about how there is no "outside", but this fu*ktarded crap I have to scroll past at the bottom of every post one of your posts is making me hope for your demise.
What are these Colorado Jim things you guys are talking about? Am I on the wrong forum again?...