Try www.myelectrical.com It's more of an engineering site.
http://myelectrical.com/notes/entryid/83/motor-starting-star-deltaTry www.myelectrical.com It's more of an engineering site.
Have you checked the contacts on both starters? Is the star dropping out? I'd check some of those things first. Has the machine ever run correctly or is it a new machine?Hello,
I hope every body is good there. Well i am installing one 37kW load Star-delta motor. when my motors turns from star to delta connection my ELCB which is 4 pole 63/30mA trip. rest of all the isolator and MCB remain same. when i disconnect all the wires from the terminal block and run my panel then there is no trip in the circuit.
i connect my six wires properly and checked my star connections which are ok...
Sir this is a brand new machine..Have you checked the contacts on both starters? Is the star dropping out? I'd check some of those things first. Has the machine ever run correctly or is it a new machine?
I like the sir part:laughing::laughing: Couldn't tell that in your original post. What type of machine are you installing it on? Just curious because the machine's I've seen with star/delta starters come as a package and I presume someone test runs them before release.Sir this is a brand new machine..
Can any one please guide me what are the main cause of 4P ELCB tripping in a circuit in which i have one three phase machine running with 3core cable while neutral is only using inside the panel for control purpose such as contactors and indication lamps.I'm not sure I'm understanding the problem correctly. Is the problem that the GF breaker is tripping during the switching from star to delta?
You have an intermittent fault. A tough condition to track down.Can any one please guide me what are the main cause of 4P ELCB tripping in a circuit in which i have one three phase machine running with 3core cable while neutral is only using inside the panel for control purpose such as contactors and indication lamps.
Not everyone can just pull out a factory install 3 contactor start system and its associated wiring system and install a soft start.It's not uncommon for this to happen, it has to do with the phase shift that takes place in the transition and whether or not the magnetic field in the motor has collapsed, and/or whether the motor slows down during the open transition.
The shortest route to a solution is to scrap the star-delta starter and install a solid state soft starter, it will not have this issue and is better for the motor and load. All other potential solutions involve having someone with experience in this issue being there with the motor and starter to troubleshoot it, because it could be any of a large number of issues, or ultimately it may be that star delta will never work for your application. But you will not know until you have spent countless hours trying other solutions. So it comes down to you deciding wh[p]ether your time is more valuable than the hardware.